Hi,
Question,
in order to save money,


how about if I install a 600A service equip. with 600A class-T @ 100K AIC fuses as main and all down-stream breakers @ 10000A , still series rated all from same manuf.

would this be cost saving instead of installing 65K AIC cir. breaker as main and series rating to down -stream in-reference to available short... of 42000A given by the local utility company. ?????

tanx
1 - 6 of 6 Posts

·
RIP 1959-2015
Joined
·
10,730 Posts
Hi,
Question,
in order to save money,


how about if I install a 600A service equip. with 600A class-T @ 100K AIC fuses as main and all down-stream breakers @ 10000A , still series rated all from same manuf.

would this be cost saving instead of installing 65K AIC cir. breaker as main and series rating to down -stream in-reference to available short... of 42000A given by the local utility company. ?????

tanx
Yes you can use a fused disconnect.
 

·
Retired Account
Joined
·
39,616 Posts
Fuses take more of a punch for less $$$ Tamas.

But not all fuses are created equal, so some research may be prudent

for instance, the RK5's come with a rejection piece that can be installed to prevent lesser AIC fuses into a disco

~CS~
 

·
Registered
Joined
·
20,120 Posts
Hi,
Question,
in order to save money,


how about if I install a 600A service equip. with 600A class-T @ 100K AIC fuses as main and all down-stream breakers @ 10000A , still series rated all from same manuf.

would this be cost saving instead of installing 65K AIC cir. breaker as main and series rating to down -stream in-reference to available short... of 42000A given by the local utility company. ?????

tanx
Its done all of the time. ;)
 