I am looking for a fuse puller that can pull out a big knife type fuse out of a holder. The fuse is roughly the size of a rockstar can, slightly taller than a regular soda can.

I found an ideal one that can pull a fuse 2.5" in diameter, just wondering if there is something better that you guys use.
 

·
Ambassador of Amps
Joined
·
9,518 Posts
Discussion Starter · #5 ·
Your pulling fuses while energized???

Why???
the fuses ARE the service disconnect. Im dealing with 220VDC straight from the POCO. I can kill the load down the line so im not removing them under any load, but they are still energized.
 

·
Registered
Joined
·
6,189 Posts
Huh? It was my understanding the disconnect switch was to the line side of the fuses, so that they can be pulled under no load. So if you throw the disconnect open, there is no voltage present at the fuses. Do you just have a special disconnect or something?
 

·
Ambassador of Amps
Joined
·
9,518 Posts
Discussion Starter · #7 ·
come on guys.. im dealing with a building built in 1909. it is what it is. if I have to put a glove on and yank them out, i will.

My special disconnect is a 2x4' asbestos lined JB, with 2 giant fuse holders in them. PGE conductors are wrapped with string and just enter the box through a KO.
 

·
Registered
Joined
·
5,687 Posts
TOOL_5150 said:
come on guys.. im dealing with a building built in 1909. it is what it is. if I have to put a glove on and yank them out, i will. My special disconnect is a 2x4' asbestos lines JB, with 2 giant fuse holders in them. PGE conductors are wrapped with string and just enter the box through a KO.
Time to invest in a arc flash suit and mask buddy.
I'll admit to some pretty unsafe practices in the past but not anymore. At least put the thought on the back burner. Everything only goes right x many times in a row.
 

·
Registered
Joined
·
2,519 Posts
come on guys.. im dealing with a building built in 1909. it is what it is. if I have to put a glove on and yank them out, i will.

My special disconnect is a 2x4' asbestos lined JB, with 2 giant fuse holders in them. PGE conductors are wrapped with string and just enter the box through a KO.
Got pics?

Stay safe, call for a POCO work with.
 

·
Ambassador of Amps
Joined
·
9,518 Posts
Discussion Starter · #10 ·
Time to invest in a arc flash suit and mask buddy.
I'll admit to some pretty unsafe practices in the past but not anymore. At least put the thought on the back burner. Everything only goes right x many times in a row.
I wont admit to the unsafe things ive done in just the past year, at least not here, but you are very right.. luck does run out. Probably time to invest in some real PPE.
 

·
Ambassador of Amps
Joined
·
9,518 Posts
Discussion Starter · #11 ·
Got pics?

Stay safe, call for a POCO work with.
Let me dig them up... I cant remember if I took pics of the AC or DC main JB in this building.

This building has a 3 phase delta 120/208 AC service and 110/220 DC service, specifically for the elevator.
 

·
Ambassador of Amps
Joined
·
9,518 Posts
Discussion Starter · #13 ·
I dont have any pics of this JB, but i can take some next time in there... within a week.

Here are some pics of the elevator equipment, and its Kwh meter and disconnects.










 

·
antisocial group ******
Joined
·
773 Posts
Mr. Tool,

I do not like the ideal yellow pullers for this size, they either release the fuse half pulled, or bend your hands toward the holder during the re-insertion process. I have on occasion had to pull fuses under (minimal as I could make them) load, and certainly while energized.

But DC as you know is a different animal, having no zero crossing point. I will never pull one under any type of load, and will not pull one until I have read the amp meter for myself.

Now being on this forum I cannot recommend anything outside of absolute child proof safety measures. So I wont.

But I have heard that some people will insulate the handles on a large set of channel locks with many layers of electrical tap, and do the same thing to the jaws of these large channel locks and pull the fuses. One hard quick jerk and follow through with the arm to quickly break any arc that may follow.

Thats what I hear anyway.
 

·
Ambassador of Amps
Joined
·
9,518 Posts
Discussion Starter · #16 ·
Mr. Tool,

I do not like the ideal yellow pullers for this size, they either release the fuse half pulled, or bend your hands toward the holder during the re-insertion process. I have on occasion had to pull fuses under (minimal as I could make them) load, and certainly while energized.

But DC as you know is a different animal, having no zero crossing point. I will never pull one under any type of load, and will not pull one until I have read the amp meter for myself.

Now being on this forum I cannot recommend anything outside of absolute child proof safety measures. So I wont.

But I have heard that some people will insulate the handles on a large set of channel locks with many layers of electrical tap, and do the same thing to the jaws of these large channel locks and pull the fuses. One hard quick jerk and follow through with the arm to quickly break any arc that may follow.

Thats what I hear anyway.
The channellock idea crossed my mind yesterday... I can definitely achieve zero load, but didnt want to deal with the issues of re-installing the fuses.

Ive also thought of maybe getting 2 of the ideal fuse pullers to keep the pressure more even, but even that sounds sketchy.
 

·
Ambassador of Amps
Joined
·
9,518 Posts
Discussion Starter · #18 ·
This, Have them turn it off and put the correct disconnect in.




If you turn it off , you don't need to buy the PPE.
I have no valid excuse for not turning it off, other than the matter is mostly out of my hands. I did a FOP, with unfortunately not much load, all readings were the same except for 1 fuse holder down the line, which I was able to make tighter and dropped the mV down to the other readings.
 

·
antisocial group ******
Joined
·
773 Posts
The channellock idea crossed my mind yesterday... I can definitely achieve zero load, but didnt want to deal with the issues of re-installing the fuses.

Ive also thought of maybe getting 2 of the ideal fuse pullers to keep the pressure more even, but even that sounds sketchy.
It works well for re-install also.

If they are tanged fuses, snap in the dead side first, that will line everything up- then swing it in.

If they are round fuse clips, line up on the dead side and clip it in.

Channel locks have a much more assured feel and I am told work better then anything else in this type of situation.

But I would have Poco pull it all down first.
 