Electrician Talk banner

Gas line bonding, BC

CEC 
4K views 23 replies 12 participants last post by  vhk 
#1 ·
Inspector wants the gas line in a commercial kitchen bonded. There’s an EMT run next to the gas line but he won’t let me bond to that, he says it needs to go to the panel. I’m not going to fight him on it, I’m just wondering why. I’m in a new town and I don’t want to get on the wrong side of an inspector so I’m asking you guys. 😊
 
#7 · (Edited)
Is there some special amendment in that province?

Like nrp3 mentioned, gas appliances are already bonded through the wiring so a threaded gas pipe to the appliance does not need another bond

This is from 2021 Canadian code 10-700 Appendix B

“It should also be noted that the requirement in Rule 10-700 c) to provide equipotential bonding to a
metal gas piping system is not intended to apply to metal gas tubing. Attempts to bond metal gas tubing
with conventional bonding means can create a hazardous situation where the tubing can be punctured
by installation of the bonding means or by arcing between improperly secured bonding means during
faults or lightning strikes
 
#8 ·
Is there some special amendment in that province?

Like nrp3 mentioned, gas appliances are already bonded through the wiring so a threaded gas pipe to the appliance does not need another bond

2021 Canadian code 10-700 Appendix B

It should also be noted that the requirement in Rule 10-700 c) to provide equipotential bonding to a
metal gas piping system is not intended to apply to metal gas tubing. Attempts to bond metal gas tubing
with conventional bonding means can create a hazardous situation where the tubing can be punctured
by installation of the bonding means or by arcing between improperly secured bonding means during
faults or lightning strikes
Yes, it appears to be a BC thing. These are strictly gas appliances, no wiring.
 
#14 · (Edited)
It's not well written, but like most equipotential bonding you have to take a #6 back to your grounding bus in your main distribution. The key here is also that a conductor is always being referenced. No substitute for the conductor is made. There are some random ones where you can just connect to the structure, but that's only for livestock barns. Maybe gas is less used in BC than yee-haw Alberta. Here its the base building electricians job to bond them after the meters since the gas piping for the RTU(AHU)'s is done at that point and a kitchen normally gets in early on a build to ensure they can get the power and gas supply they need. Had some small jurisdictions not even allow the connection indoors, clamp had to be outside after the meter.

For the appendix B 10-700 people are missing the key word in there... tubing. Like NPR mentioned "the stainless flex stuff" or normally here yellow (maybe pvc) coated flexible gas tubing. We don't have to bond that because there is no safe way to do it. A clamp would just crush it. But the tubing will only be between a wall outlet and the kitchen appliance.
First shot sucks, seconds pretty good. Example of what I tried to describe. In both cases the #6 is coming through the wall, it's not just the lines being tied together. Second one is a KFC I did. The base guy was a joke. All his exterior sconces were DAMP rated, couldn't understand why the inspector failed him and was forcing him to install gaskets on all of them. 🤣
 
#15 ·
It's not well written, but like most equipotential bonding you have to take a #6 back to your grounding bus in your main distribution.
Care to supply a code reference?

The key here is also that a conductor is always being referenced. No substitute for the conductor is made.
Second last paragraph of 10-700 in Appendix B may be of interest to you.

Maybe you have code amendments on these in British California?
 
#19 ·
It is an inspector requirement here in Southern Alberta to run it back to the panel as well, despite there not being a specific rule for it. The reasoning they give is to reduce the chance of having the bond path interrupted. I've questioned it after being called on it awhile back because I ran some #6 from a gas line to a nearby junction box and tied it into the bond wire there. Theoretically that should have been sufficient as there is no provision in the code that calls for it to be installed back to the service. There is, however, a mention in the Standata for bonding gas lines that suggests the bond be run back to the service or grounding electrode. It wasn't a hill to die on so that is the way it gets done now.
 

Attachments

#21 ·
I'm not arguing the reasoning, and I agree that running back to the service is the best practice. My point was that it is an inspector requirement, not a code or amendment. The amendment here in Alberta does suggest to do it a certain way, but does not make it a requirement, and there may or may not be something similar in BC. This all goes back to the OP's question where someone working out of their normal area and not familiar with the local inspector may do things that are technically acceptable (and may be acceptable in other areas), but will still get you a violation from that particular inspector.
 
#22 ·
Let's use the example of a mobile home. Panel is at one end, lets say the back. You drop a #6 down to bond the frame.

Now some gas gets added at the front of the home. Code allows you to bond that gas to the nearest part of the plane with any material suitable for that connection. Around here that is a pipe clamp and a proper connection to the frame.

It's not likely anyone will remove the frame in the future so is it necessary to run the length of the home with a #6?
 
  • Like
Reactions: Kevin
#23 ·
Let's use the example of a mobile home. Panel is at one end, lets say the back. You drop a #6 down to bond the frame.

Now some gas gets added at the front of the home. Code allows you to bond that gas to the nearest part of the plane with any material suitable for that connection. Around here that is a pipe clamp and a proper connection to the frame.

It's not likely anyone will remove the frame in the future so is it necessary to run the length of the home with a #6?
I like your example, because that is no different than bonding to a steel building. The steel the line is bonded to won't disappear without the rest of the building disappearing too!
 
This is an older thread, you may not receive a response, and could be reviving an old thread. Please consider creating a new thread.
Top