Hey Gang,

I and most of you have seen this Gas/Oil Emergency Switch (see pic below) on the stairs leading to the basement or near said equipment if the house is on a slab (sans basement).

Are there any code references to it's placement?

I have a situation where it is located in a stairwell to a basement where the gas furnace is. The stairs are being demolished and it is being turned in a storage pantry with a floor, shelves and the original door.

Can I leave it in there or do I need to move it to the new stairs/stairwell?

Thanks!
 

Attachments

· Registered
Joined
·
1,081 Posts
duque00 said:
Hey Gang, I and most of you have seen this Gas/Oil Emergency Switch (see pic below) on the stairs leading to the basement or near said equipment if the house is on a slab (sans basement). Are there any code references to it's placement? I have a situation where it is located in a stairwell to a basement where the gas furnace is. That stairwell is being demolished and is being turned in a storage pantry, complete with the original door. Can I leave it in there or do I need to move it to the new stairs/stairwell? Thanks!
i dont know if its a local thing but we dont see it any different way around here. Can you splice and send a two wire switch to the new location?
 

· Keeper Of The Magic
Joined
·
415 Posts
Discussion Starter · #5 ·
Is that so?

My parents live in Queens and it's in the stairwell to the basement. Also here on Long Island it's in the stairwell unless like I said it's on a slab.

Then again I've seen 2 switches - 1 at the top of the stairs and a 2nd on near the equipment (service switch).

Always the Emergency switch - the service switch is usually done by the plumber with the restricted license.

I always took the emergency switch to be use either by the HO or the local FD - that's it!
 

· Registered
Joined
·
1,081 Posts
duque00 said:
Is that so? My parents live in Queens and it's in the stairwell to the basement. Also here on Long Island it's in the stairwell unless like I said it's on a slab. Then again I've seen 2 switches - 1 at the top of the stairs and a 2nd on near the equipment (service switch). Always the Emergency switch - the service switch is usually done by the plumber with the restricted license.
city mightve changed in recent times, a job i was on a few years back got tagged for putting the emergency switch at the top of the stairs. We only do a few jobs in queens here and there , so i dont dive into all the code ammendments, i just do what im told is normal there
 

· Retired Account
Joined
·
39,616 Posts
The fire marshals here insist on a shutoff @ the unit, and then one outside the door entering into the furnace room.

This usually doesn't go over well in mama's kitchen, but they validate by claiming that in a fire situation one should not be opening a door to the fire and looking for a switch in the smoke, etc

there is no nec ref that i know of as to specific placement


~CS~
 

· animal lover /rat bastard
Joined
·
13,504 Posts
this is an old post from another forum, not sure what current code is:

See NFPA 31:
10.5.1*
Oil burners, other than oil stoves with integral tanks, shall be provided with some means for manually stopping the flow of oil to the burner. Such device or devices shall be placed in a readily accessible location at a safe distance from the burner.
10.5.1.1 For electrically powered appliances, the requirement of 10.5.1 shall be accomplished by an identified switch in the burner supply circuit, placed near the entrance to the room where the appliance is located.
10.5.2
An electrical service disconnect switch, arranged to stop and start the oil burner, shall be installed at the appliance. It shall be located so that it is within easy reach of the service technician for control of the oil burner while observing the flame.
 

· Keeper Of The Magic
Joined
·
415 Posts
Discussion Starter · #9 ·
Interesting Wildleg.

This is a gas situation, not oil, my bad - should of been upfront about that.

I am a big fan of the 2 switch operation anyway. I think I am going to just splice a wire at the old switch and run a new cable to the new stairwell and be done with it.

TBH - I don't even remember if there is a service switch near the furnace.
 

· Registered
Joined
·
100 Posts
If it's a disconnect for the boiler you must put it right outside the room that contains the boiler. If for some reason that door is an exterior door it must be right inside as you open the door, meaning very accessible. And yes it must be that red cover with the wording.

As for the disconnect at the boiler not sure if one is required but couldn't hurt to put one. Obviously just in series with the one at the top of the stairs.
 

· Keeper Of The Magic
Joined
·
415 Posts
Discussion Starter · #15 ·
The basement is unfinished. There is nothing down there except the furnace/HW heater and laundry.

The current stairwell is going to be closed up and the stairs demolished. A new stairwell/opening will be created in another part of the house.

I am just going to move the switch from the current location to the new location.
 

· Registered
Joined
·
100 Posts
Yes I don't know the code number but it's required, gas or oil doesn't matter. I work for one of the larger boiler companies here in NYC. Now with that said if you're not getting an inspection I wouldn't bother moving it, I assume the wires are cut to the box inside and so it would be hard to fish new wires for a switch. I say keep it where it is.
 

· Keeper Of The Magic
Joined
·
415 Posts
Discussion Starter · #19 ·
Samc - job is getting inspected. Even if I left in - it's becoming a food pantry/storage.

I think it would look pretty bad if I had to hang a sign on the outside of the door that said "Emergency Gas Cutoff Switch Inside on the Left"

Lol....
 

· Keeper Of The Magic
Joined
·
415 Posts
Discussion Starter · #20 ·
Bmail - I've seen them before - a little dated, but have seen them.

Wouldn't you want 1 switch to kill all 3 - in case of emergency?

1 Emergency and then maybe 3 service switches (1 for each), so they can be shut down locally instead of globally?
 