So I took over this job from another guy who did all the underground. There's a main building and 100 yards away sits the CT, Main Disconnect, Transfer switch and Generator.
Now the pad with all the service equipment will have a ground ring and that's what he's going to use for his electrode, which is fine. Except that he wants to put all the elctrodes in the building(ufer, water pipe, and steel) under the ground bus in the MDP.
It all sounds like it will work the same, but I thought for sure that the GEC only lands at the Target and never anywhere else? Shouldn't the building electrodes go out and tie in with the ring and all land in the same spot together? I'm just having a hell of a time finding a refference.
Thanks