Alot of people use kenny clamps , plastic romex connector or metal romex connectors. Should any one of these not be used?
Kenny clampWhat's a Kenny Clamp?
<crap>, 30 odd years ,and i just realizing i'm doing it wrong...NM connectors are not listed for a single conductor. They are only listed for type NM cable. that's the issue with using NM connectors for the GEC.
It is posts like this that really get me thinking about stuff that we have done for years and have never really thought about it. We cannot just drill a hole in a meter socket or panel; stick the wire in and tie it in. Did that a few times over the years and the inspector stated without hesitation that you must use a connector when entering a cabinet or box… so off we go using a plastic or two-screw connector… and the world continues to spin effortlessly…NM connectors are not listed for a single conductor. They are only listed for type NM cable. that's the issue with using NM connectors for the GEC.
Why not?We cannot just drill a hole in a meter socket or panel; stick the wire in and tie it in.
Uh oh...I have about 12 million of them out there in that application. :whistling2:As far as the Kenny clamp , There are less expensive listed products on the market. Arlington Industries makes 2 and I believe Bridgeport makes one.
NM connectors are not listed for a single conductor. They are only listed for type NM cable. that's the issue with using NM connectors for the GEC.
Busted! I'll be alerting all the inspectors in your area first thing tomorrow morning that you are altering the UL listed equipment by drilling a hole in it. A clear and present danger and obvious NEC code violation.Why not?
Many panels have a small hole for that purpose. And there is nothing stopping us from making our own holes.
The GEC is different than everything else. Support, burial depth, etc.
I told you I was hardcore.Busted! I'll be alerting all the inspectors in your area first thing tomorrow morning that you are altering the UL listed equipment by drilling a hole in it. A clear and present danger and obvious NEC code violation.![]()
Post that article.Per the NEC, the GEC has to be BONDED when it passes through a ferrous enclosure.
Link?This was detailed - by me - in a thread less than two-weeks ago.
We are abiding by the NEC, which does not require the GEC to be bonded as it enters an enclosure. The only thing even remotely close to what you are saying is that the GEC needs to be "choked" as it enters and exits a metal raceway.But hey, as long as your AHJ is letting you get by... why obey the NEC ?
No, your logic of saying things are required without citing the code is what handymen do.Hey, that's the same logic as every DIY// handy man out there.
No, using any of those is a waste of money, effort, and natural resources, run it though one of the factory supplied holes or drill your own and land it in a lug bonded to the enclosure.Alot of people use kenny clamps , plastic romex connector or metal romex connectors. Should any one of these not be used?
The GEC has to land on the neutral bar.No, using any of those is a waste of money, effort, and natural resources, run it though one of the factory supplied holes or drill your own and land it in a lug bonded to the enclosure.
Roger
My post is relating to this connection being made in the meter can which is the norm in the Southeast. The lug I'm referring to is the factory supplied Neutral bar in the meter can which has provisions for the GEC along with the line and load side neutrals and is factory bonded to the enclosure.The GEC has to land on the neutral bar.
The exception is that you can land it on the ground bar if the main bonding jumper is an appropriately sized wire or busbar.
Landing the GEC to a lug bonded to the metal enclosure when the main bonding jumper is just a screw is not compliant.