Hi all got a good one we could you the collectives thoughts and ideas on. Scenario: Small Sq D homeline 6 ckt sub panel in a small apartment with breakers randomly turning off, not tripping. Utility thought it may be their end, after trouble shooting and running a recording they said it was customer side.
What we've tried-
Pulled apart every device, inspectected and remade each connection.
Isolated and checked each circuit including panel feed from main for direct shorts- hot to hot, hot to neutral, hot to ground none found.
Thermal scanned panel for hot spots- none found
Megged each wire all check ok.
Replaced Main Breaker, and branch circuit breakers.
Moved branch circuit wires from one side of panel to other side. swapped breakers around to different locations. Breakers still turning off on their own not tripping.
Replaced all GFCI's.
With no load the breakers will still turn themselves off. It has done it twice while we were standing there watching the panel. Called Sq. D, they said the breakers can't do what they're doing. Which I used to say the same myself. I stopped charging these folks long ago now I just need to know what it is. I have 35 years in this trade and my dad who retired with 50 used to tell me when I was an apprentice- "Troubleshooting electricity is never magic or a mystery, it's always the one simple thing you overlooked". HELP- what are we not seeing? Next step is a Priest and some sage!
What we've tried-
Pulled apart every device, inspectected and remade each connection.
Isolated and checked each circuit including panel feed from main for direct shorts- hot to hot, hot to neutral, hot to ground none found.
Thermal scanned panel for hot spots- none found
Megged each wire all check ok.
Replaced Main Breaker, and branch circuit breakers.
Moved branch circuit wires from one side of panel to other side. swapped breakers around to different locations. Breakers still turning off on their own not tripping.
Replaced all GFCI's.
With no load the breakers will still turn themselves off. It has done it twice while we were standing there watching the panel. Called Sq. D, they said the breakers can't do what they're doing. Which I used to say the same myself. I stopped charging these folks long ago now I just need to know what it is. I have 35 years in this trade and my dad who retired with 50 used to tell me when I was an apprentice- "Troubleshooting electricity is never magic or a mystery, it's always the one simple thing you overlooked". HELP- what are we not seeing? Next step is a Priest and some sage!