Hey Gang, I need your thoughts on this.
bonding of a Gland on armored cable is done largely for reducing the "touch potential" that can be induced into the Armour of an AC cable. Cables under 400 amps are typically bonded at both ends, while over 400 amps are only on one end. What I am questioning is the bonding of glands on signal cables (instrumentation), now if there was "clean earth" availability I wouldn't even pose this, but bonding the gland to the same earthing system used by large motor systems seems to be in contrast to bonding to eliminate "Noise".
in addition, if a massive fault were to occur, it is possible to distribute a portion of that fault current to the critical ESD systems is it not.
Nothing I can see in the wide world of Google, clearly points out why we would bond the signal cabling to the "Dirty Earth" system. I'm looking for real answers here guys as the way bonding is done over here in the middle east is ugly and expensive.
Cheers
bonding of a Gland on armored cable is done largely for reducing the "touch potential" that can be induced into the Armour of an AC cable. Cables under 400 amps are typically bonded at both ends, while over 400 amps are only on one end. What I am questioning is the bonding of glands on signal cables (instrumentation), now if there was "clean earth" availability I wouldn't even pose this, but bonding the gland to the same earthing system used by large motor systems seems to be in contrast to bonding to eliminate "Noise".
in addition, if a massive fault were to occur, it is possible to distribute a portion of that fault current to the critical ESD systems is it not.
Nothing I can see in the wide world of Google, clearly points out why we would bond the signal cabling to the "Dirty Earth" system. I'm looking for real answers here guys as the way bonding is done over here in the middle east is ugly and expensive.
Cheers