I would say that both yourself and your electrical inspector are confused as to proper code methods. You need the service disconnect since you have more than 6 turns of the hand to disconnect power at the service for the building, that is why there is a service switch ahead of all the metering. Each meter does not need its own ground , but all equipment belonging to the service must be bonded together, tied to the neutral at the service and the service needs to be grounded to all grounding electrodes present at the service, including a metal water pipe in direct contact with soil for ten feet if present at the building.