if i run 3 sets of parallel feeders into my mdp each in its own ridged nipple will my bonding bushing ground on each of them be sized on that nipples amperage or does it need to be rated to the total amperage of all three sets
A single common continuous equipment bonding jumper shall be permitted to connect two or more raceways or cables where the bonding jumper is sized in accordance with Table 250.122 for the largest overcurrent device supplying circuits therein.
if i run 3 sets of parallel feeders into my mdp each in its own ridged nipple will my bonding bushing ground on each of them be sized on that nipples amperage or does it need to be rated to the total amperage of all three sets