That does not make it a neutral, and the system will operate without this neutral ground bond. And even when you do bond it, you do not need a grounding electrode for normal operation.
Did I say that? I thought I said the electrode puts the neutral at the same potential as ground.
 

·
Registered
Joined
·
31,325 Posts
Discussion Starter #24
Unless you have a ground connection to the neutral all you have is a center tap, not a neutral.
Did I say that? I thought I said the electrode puts the neutral at the same potential as ground.
I do not want to put words in your mouth BUT.......
 

·
Administrator
EC
Joined
·
22,591 Posts
IMO, the purpose of the grounding electrode conductor is simply to drain any voltage spikes to the earth rather than thru the house. Ground rods in most areas are not very useful but a concrete encased electrode can be beneficial to accomplish this goal.

Brian, I have had many electricians tell me that the grounding electrode conductor is there in case the neutral fails.... And these were licensed guys. Grounding is probably the hardest thing to understand in the nec
 

·
Registered
Joined
·
31,325 Posts
Discussion Starter #26
Holt is long winded but man you forget how knowledgeable he is.
I am not talking safety, I am not talking NEC, I am asking how many electricians on this forum think an AC or DC distribution system will work without a metal rod stuck into the Earth.

I have had several discussions that turned into arguments with electricians that insisted you need a ground rod for an electrical distribution system to operate. I was amazed at their lack of knowledge and common sense. In the end, my last comments are how to airplane electrical systems operate and come to my office I'll do a setup and prove you wrong. They basically told be F' off or ignored me.

I would bet most electricians on a forum know better because they bother to belong to a forum to discuss the trade. But do a poll at work and ask fellow electricians.

Does a power system need to be grounded to Earth to work?
 

·
Band Member
DIYer Extrodinaire
Joined
·
7,158 Posts
Well, everyone knows electricity wants to go to ground :p
 
  • Like
Reactions: Bird dog

·
Registered
Joined
·
6,985 Posts
. In the end, my last comments are how to airplane electrical systems operate and come to my office I'll do a setup and prove you wrong. They basically told be F' off or ignored me.
Ask them where the ground rod is for their truck...:unsure::D
 
  • Like
Reactions: ohm it hertz

·
Administrator
EC
Joined
·
22,591 Posts
Grounding is not necessary as there are ungrounded systems.
 

·
Registered
Joined
·
6,985 Posts
  • Like
Reactions: brian john

·
Registered
Electrician
Joined
·
1,414 Posts
I think it is soooooooo important that the NEC requires a ground rod to be at less than 25 ohms resistance to ground and if it is not you need two rods. But don't bother testing the second rod as it doesn't matter, it will be fine, hahahahahah,
 

·
Registered
Joined
·
6,985 Posts
I think it is soooooooo important that the NEC requires a ground rod to be at less than 25 ohms resistance to ground and if it is not you need two rods. But don't bother testing the second rod as it doesn't matter, it will be fine, hahahahahah,
Just drop two rods & be done with it.
 
  • Like
Reactions: SparkyBB

·
Administrator
EC
Joined
·
22,591 Posts
I think it is soooooooo important that the NEC requires a ground rod to be at less than 25 ohms resistance to ground and if it is not you need two rods. But don't bother testing the second rod as it doesn't matter, it will be fine, hahahahahah,
Yes, Imo it would take forever to get under 25 ohms with rods however a concrete encased electrode can get there easily. I measured my concrete encased electrode years ago and got 13 ohms. I had 2 rods at the same site and I had 89 ohms.....

I don't understand why people fight the concrete encased electrode. In NC they amended it so you don't have to install a concrete encased electrode. We always did unless the builders forgot. We had to stay ontop of that.
 
  • Like
Reactions: MotoGP1199

·
Registered
Joined
·
6 Posts
How many electricians feel grounding a service is necessary for operation, not bonding, but grounding to an electrode?

It seems that some electricians feel a connection to earth is a necessity for an AC power system to operate.
Depends on the type of system. If theres controls involved an ungrounded neutral could cause unpredictable actions in control circuits. In distribution systems it will not have an effectect in unbalanced systems it can cause overheating if the sum of the loads not equal 0
Sent from my F8331 using Tapatalk
.
 

·
Registered
Joined
·
6,985 Posts
....
 

·
Registered
Electrician
Joined
·
1,414 Posts
Yes, Imo it would take forever to get under 25 ohms with rods however a concrete encased electrode can get there easily. I measured my concrete encased electrode years ago and got 13 ohms. I had 2 rods at the same site and I had 89 ohms.....

I don't understand why people fight the concrete encased electrode. In NC they amended it so you don't have to install a concrete encased electrode. We always did unless the builders forgot. We had to stay ontop of that.
Yep I agree, a concrete encased electrode is a much better option. If its new construction, its already available. Concrete works so well, you can merely splash water on a pool deck and check continuity back to the light junction box or anything else bonded to the pool shell with one lead on the wet concrete.

As to the original post a connection to earth is not necessary for a system to function properly under normal conditions. It helps with other issues that arise like static voltage discharge, etc. There was a post recently on here with examples of ungrounded transformer secondary's that were required by NEC to be un-grounded. All of those systems operate just fine without a connection to the earth. Bonding is far more important for safety, proper boding will clear a fault on branch circuits and feeders.
 

·
Registered
Joined
·
916 Posts
I am not talking safety, I am not talking NEC, I am asking how many electricians on this forum think an AC or DC distribution system will work without a metal rod stuck into the Earth.

I have had several discussions that turned into arguments with electricians that insisted you need a ground rod for an electrical distribution system to operate. I was amazed at their lack of knowledge and common sense. In the end, my last comments are how to airplane electrical systems operate and come to my office I'll do a setup and prove you wrong. They basically told be F' off or ignored me.

I would bet most electricians on a forum know better because they bother to belong to a forum to discuss the trade. But do a poll at work and ask fellow electricians.

Does a power system need to be grounded to Earth to work?
I agree, I think they forget that voltage is between 2 points and if it's voltage to ground you have to have a ground reference. But with no reference to ground it operates just fine. A classic, simple example is the old school 2 prong razor receptacle.
I will add that many, far better electricians than me, make that mistake.
 

·
Registered
Electrical Contractor
Joined
·
1,970 Posts
How many electricians feel grounding a service is necessary for operation, not bonding, but grounding to an electrode?

It seems that some electricians feel a connection to earth is a necessity for an AC power system to operate.
Well sure, in an intact service, excluding the supply, and an installation in good repair, it will work just fine without an electrode.


:) Have you ever clamped a GEC and found current flowing on it?
 

·
Registered
Joined
·
31,325 Posts
Discussion Starter #39
Well sure, in an intact service, excluding the supply, and an installation in good repair, it will work just fine without an electrode.


:) Have you ever clamped a GEC and found current flowing on it?
As part of my job I do grounding investigations, so yes
 

·
Registered
Joined
·
31,325 Posts
Discussion Starter #40
Depends on the type of system. If theres controls involved an ungrounded neutral could cause unpredictable actions in control circuits. In distribution systems it will not have an effectect in unbalanced systems it can cause overheating if the sum of the loads not equal 0
Sent from my F8331 using Tapatalk
.
Yep, we had a site that was impedance grounded and the UPS's worked but would not parallel.
 