So would you agree that a ground electrode serves purposes other than to dissipate lightning? I mean, if that current wasn't on that electrode it might be going through a person....As part of my job I do grounding investigations, so yes
So would you agree that a ground electrode serves purposes other than to dissipate lightning? I mean, if that current wasn't on that electrode it might be going through a person....As part of my job I do grounding investigations, so yes
Impedance grounded is still grounded. The neutral from the star point still feeds the circuit from the top of the impedance and at the bottom of the impedance it goes to ground where al your other grounded components are bonded to.Yep, we had a site that was impedance grounded and the UPS's worked but would not parallel.
The impedance just limits the amount of earth fault current when an earth fault arises.Yep, we had a site that was impedance grounded and the UPS's worked but would not parallel.
Yes I know what an Impedance grounded system is, BUT UPS's did not like it and would not work, did you not see that in my post?Impedance grounded is still grounded. The neutral from the star point still feeds the circuit from the top of the impedance and at the bottom of the impedance it goes to ground where al your other grounded components are bonded to.
Sent from my F8331 using Tapatalk
Wonder why it would not work.Yes I know what an Impedance grounded system is, BUT UPS's did not like it and would not work, did you not see that in my post?
At the previous r-mix company I worked at, they have 3 floating 480 Deltas. A year and a half ago one control trailer burned up at night, after what I finally found out to be a primary to secondary short. It was a sub metering setup from a primary metered mine power. When I got there the mine superintendent was flipping out because we were on the same bank as his test lab and it was winter. I thought the fire shorted the secondary drop and blew the cutouts.I did not think that's what they're talking about in 250.4, I think the idea is, when one of the current carrying conductors on the system is at ground potential, the phase-to-ground potential is limited, so in the event of a strike to ground or a utility high voltage fault to ground, less damage occurs to the system and to the building and the people in it.
True or false?
To these owners, maintenance is a necessary evil.At the previous r-mix company I worked at, they have 3 floating 480 Deltas. A year and a half ago one control trailer burned up at night, after what I finally found out to be a primary to secondary short. It was a sub metering setup from a primary metered mine power. When I got there the mine superintendent was flipping out because we were on the same bank as his test lab and it was winter. I thought the fire shorted the primary drop and blew the cutouts.
Uhh no, I fused the cutouts and closed them then shut the knives at the road. All was great for about 5 seconds then the RR RRR RRRR RRRRR RRRRRR!!!!! The circulating current was taking off like mad! I barely opened the knives in time to keep the xformer from completely blowing.
I tried every way possible to explain to the owners what happened, but I couldn’t get through to them about the hazards of a floating Delta and why a corner ground is important.
And I was some sort of practitioner of a dark art. Ultimately their view became, if I don’t understand it, it’s unimportant. If you want some real hair raising stories, send me a PM. That one is really tame by contrast.To these owners, maintenance is a necessary evil.
One story I heard was about a jbox cover blowing off in a break room (maybe a 3x3?). smhAnd I was some sort of practitioner of a dark art. Ultimately their view became, if I don’t understand it, it’s unimportant. If you want some real hair raising stories, send me a PM. That one is really tame by contrast.
Great line. Maybe make that your signature.And I was some sort of practitioner of a dark art.
Arrrrr. In your best Robert Newton pirate voice.One story I heard was about a jbox cover blowing off in a break room (maybe a 3x3?). smh
Great line. Maybe make that your signature.
Old ship maps...past here there be sea monsters...
NOPE, If it was not there it would be somewhere else, if the service is bonded to the H20 and there is sufficiently low resistance to allow current to flow all you have done is set up a current loop or this could be parallel current from the utility transformer to the main service. But what you are stating is seldom seen due to Earth resistance usually you will see the current on water pipes that are shared from places that have their own services.So would you agree that a ground electrode serves purposes other than to dissipate lightning? I mean, if that current wasn't on that electrode it might be going through a person....
I was not asking this, though my question was a little open to interpterion.I am not super solid on this but I think that the grounding system and a low-impedance ground are important for operation of MOV type surge protection that shunts surges to ground.
I did not think that's what they're talking about in 250.4, I think the idea is, when one of the current carrying conductors on the system is at ground potential, the phase-to-ground potential is limited, so in the event of a strike to ground or a utility high voltage fault to ground, less damage occurs to the system and to the building and the people in it.
True or false?
It depends upon where the earth grounds fall within the gradient created by the strike.I was not asking this, though my question was a little open to interpterion.
In Theory true but what are the odds that a 8' rod driven in the ground connected to a #6 CU will dissipate the surge? Take a residential service Want about the 4/0 Aluminum neutral feeding back to the transformer all all the driven electrodes on the utility distribution, which one has lower impedance?
In absence of metallic water piping or "some other place" an electrode is the place where an objectionable current should be.NOPE, If it was not there it would be somewhere else, if the service is bonded to the H20 and there is sufficiently low resistance to allow current to flow all you have done is set up a current loop or this could be parallel current from the utility transformer to the main service. But what you are stating is seldom seen due to Earth resistance usually you will see the current on water pipes that are shared from places that have their own services.
It Depends on the duration and energy of the strike ANDIt depends upon where the earth grounds fall within the gradient created by the strike.
Sent from my iPad using Tapatalk
HOW? WHY?In absence of metallic water piping or "some other place" an electrode is the place where an objectionable current should be.
So what were some of the circumstances that led to you measuring current on a GEC?
Works fine until a Squirrel eats throughHow many electricians feel grounding a service is necessary for operation, not bonding, but grounding to an electrode?
It seems that some electricians feel a connection to earth is a necessity for an AC power system to operate.
The ground rod on the truck is the frame. ; )Ask them where the ground rod is for their truck...![]()