Discussion Starter · #1 ·
Hello, this is my first post so forgive if i ramble a bit as i am new here.
I am wiring a 3 phase delta wye transformer that has a copper bonding strap installed from the manufacturer. I installed a double lug and bolted it to the cage and terminated the grounds from the primary and secondary in this location, I then put a double lug on Xo where i terminated the secondary neutral and the bonding wire i brought to the building steel.
Question, is this correct or should i have terminated the primary, secondary grounds AND the bonding wire i brought to building steel under the same lug and brought a jumper from said lug and connected that to the X0?
 

·
Registered
Joined
·
3,353 Posts
I am wiring a 3 phase delta wye transformer that has a copper bonding strap installed from the manufacturer.
Theres a good chance that's not a bonding strap to the XO
Question, is this correct or should i have terminated the primary, secondary grounds AND the bonding wire i brought to building steel under the same lug and brought a jumper from said lug and connected that to the X0?
I usually put a 3 lug on XO.

Neutral,GEC and jumper to frame.

On frame I put 3 lug.

Jumper to XO, incoming EGC and outgoing EGC.
 
  • Like
Reactions: sparkyjim

·
Registered
Joined
·
125 Posts
Discussion Starter · #3 ·
thanks

I used to do something similar but after going over 250-30 i changed it up. 250-30(A) states that a separately derived system shall except as otherwise permitted in this article, a grounded conductor shall NOT be connected to normally non-current carrying metal parts of equipment, be connected to EGC's, or be be reconnected to ground on the load side of the system bonding jumper.
So I am unsure if I am understanding it wrong or if changing it from the way I used to is making me question myself because I used to connect a jumper from Xo to the EGC's but this is saying not to which is new language in the 2011 code.
 

·
Registered
Joined
·
3,353 Posts
I used to do something similar but after going over 250-30 i changed it up. 250-30(A) states that a separately derived system shall except as otherwise permitted in this article, a grounded conductor shall NOT be connected to normally non-current carrying metal parts of equipment, be connected to EGC's, or be be reconnected to ground on the load side of the system bonding jumper.
So I am unsure if I am understanding it wrong or if changing it from the way I used to is making me question myself because I used to connect a jumper from Xo to the EGC's but this is saying not to which is new language in the 2011 code.
The system bonding jumper is in your XFMR.

You aren't reconnecting after the jumper.
 