I just don't understand. Tell me if I am wrong. Your supply Company do not supply a dedicated ground/earth with a guaranteed impedance? You install ground/earth electrodes - but not always - if water pipes etc are available? How do you ensure impedance values sufficient to operate circuit breakers within specified times. And how do you protect against transient currents if a dedicated ground such as a rod becomes open circuited. I'm all mixed up. help
in a residential service the utility supplies 3-wire single phase 240/120 L1, L2 and the neutral/grounded conductor, they ground the neutral at the transformer.
Ground connections to earth have little or nothing to do with the operation of over current protection devices (OCP's), ground connections (bonding) from the service through out the facility insure proper operation of the OCP's.
Typical service, if copper is available they do earth connections to the copper water pipe, though thankfully this is going away. I say thankfully as this connection results in ground current on the water piping system. If there is plastic water pipe you are required to drive one rod and test for impedance if less than 25 ohms you are good, if higher that 25 ohms you must drive a second rod and that is it. Most electrician's drive two rods and are done with the earth ground connection.
We really do not care about the resistance to ground in residential applications as this connection is necessary for accidental utility primary to secondary faults (seldom happens?) and lightning strikes. Florida is the capital of the USA and possible the world for lightning strikes and their soil pretty much sucks for low resistance earth/ground connections. Lots of sand.
As for transients, other than lightning I do not see how a ground system would protect from line transients.