Im putting two disconnects side by side connected with a 2" nipple next to a two gang meter base. When I run the GEC to the first disconnect, can I then run the GEC through the nipple into the other disconnect? The nipple will have the service conductors in there as well. Or, can the nipple act as the ground?
 

· Salty Member
Joined
·
31,030 Posts
230.7 Other Conductors in Raceway or Cable. Conductors other than service conductors shall not be installed in the same service raceway or service cable.

Exception No. 1: Grounding conductors and bonding jumpers.

Exception No. 2: Load management control conductors having overcurrent protection.
 

· Registered
Joined
·
379 Posts
Discussion Starter · #3 ·
230.7 Other Conductors in Raceway or Cable. Conductors other than service conductors shall not be installed in the same service raceway or service cable.

Exception No. 1: Grounding conductors and bonding jumpers.

Exception No. 2: Load management control conductors having overcurrent protection.
Thanks. Can the ground be bare?
 

· Administrator
Retired EC
Joined
·
24,991 Posts
A warning-- Around here we often use solid copper and I got call on 310.106(C). I can see if this was a long run with bends but a short nipple...gee wiz.
 