I assure you, it is not what you think....Three places I have worked on come immediately to mind.
You are right. Different stinger voltage than I am used to.I assure you, it is not what you think....
A-120V -gd
B-215V-gd
C-120V-gd
240V between phases.
And everything in the panel works.....
I had to step away for a couple minutes....
Other than the fact that the high leg is usually closer to 208v, this is pretty much like every delta 3 phase 240v transformer I've worked on. I'm guessing you've never seen a high leg delta service?I assure you, it is not what you think....
A-120V -gd
B-215V-gd
C-120V-gd
Oh no, I've seen and worked on plenty.I'm guessing you've never seen a high leg delta service?
That is because those combinations of voltages are not actually possible. If the stinger voltage to the grounded conductor is 215, then the other two legs will have a voltage of ~124 to the grounded conductor, and the phase to phase voltage would be 248.You are right. Different stinger voltage than I am used to.
Yes, my bad....That is because those combinations of voltages are not actually possible. If the stinger voltage to the grounded conductor is 215, then the other two legs will have a voltage of ~124 to the grounded conductor, and the phase to phase voltage would be 248.
yes part of the panel is single phase ,maybe half then the remainder is three phaseView attachment 34661
The 480Vx240/120V Delta transformer
And the panel it feeds....
Haven't seen this set-up ever.....Took me a while to figure out how it works..
The whole panel is only A-C phases, yet the bus bar behind them are 3 phase including the stinger leg.In the panel picture, it looks like the spare spaces only have bus fingers for the A and C phases. Was all of the panel built like that or did some of the spaces have B phase fingers for the installation of 3 pole breakers?
I'm viewing from my phone, so I can't get a good look at the pictures. I don't ever remember seeing anyone use the highleg with single pole breakers to obtain 208v, but I have often wondered how out would work. Sounds good in theory, never been too sure about reality though.Oh no, I've seen and worked on plenty.
But I've never seen this set-up before.
Look at all the SP breakers.
Are you referring to the breaker buss terminals only being bolted to A and C phase?Dnkldorf said:I didn't even know, that who-ever did it,that it was even possible to do???
yup...Are you referring to the breaker buss terminals only being bolted to A and C phase?
Yes, as long as loading permitted and the breakers is rated straight 240.Say I have a 208 volt AC unit. Could I run 1 wire from B-phase + a neutral?