Eye lab and retail setup

I only need to use HCF in the exam room and pretest rooms, where the actual "patient" is evaluated in.

I can use MC for everything else, but it has to be routed away from the exam rooms and can not go over the ceilings above those rooms.


Do I have this correct?
 

·
RIP 1959-2015
Joined
·
39,618 Posts
Eye lab and retail setup

I only need to use HCF in the exam room and pretest rooms, where the actual "patient" is evaluated in.

I can use MC for everything else, but it has to be routed away from the exam rooms and can not go over the ceilings above those rooms.


Do I have this correct?
I don't see why you cannot have regular MC IN the ceilings.
 

·
Professional Nit Picker
Joined
·
2,339 Posts
Eye lab and retail setup

I only need to use HCF in the exam room and pretest rooms, where the actual "patient" is evaluated in.

I can use MC for everything else, but it has to be routed away from the exam rooms and can not go over the ceilings above those rooms.


Do I have this correct?
MC CAN pass through the walls and ceilings of patient care areas. It CAN NOT be used for anything in the patient care areas
 