Discussion Starter · #1 ·
What are the pros/cons of high resistance grounding versus solid grounding and low resistance grounding? What is the preference for different applications? What complications does high resistance grounding introduce in drive system applications?

Thank you.
 

· Banned
Joined
·
261 Posts
One main benefit of high resistance grounding is that if there is a ground fault, the equipment will still operate rather than trip out.

A quick example would be if you had a mission critical submersible sump pump in a grounded container. If the pump faulted in the water and energized the water, the OCPD might trip can cause a flood. If you have a high resistance ground system and have a fault, the equipment would continue to operate and there would likely be an alarm to alert personnel to the danger and that a repair needs to be made.
 

· Premium Member
Licensed Electrical Contractor
Joined
·
11,733 Posts
What are the pros/cons of high resistance grounding versus solid grounding and low resistance grounding? What is the preference for different applications? What complications does high resistance grounding introduce in drive system applications?

Thank you.
Home work? Or test question?

Either way, you tell us what you think then we'll discuss it.
 

· Registered
Joined
·
33,793 Posts
The paper mills I work at have high resistance grounds. You don't want the paper machines shutting down just because a motor fails. Especially if there is a redundant motor to take its place.
Just some wording in your post that need straitening out, if the motor fails you are shutting down, if one phase faults you will continue to run.
 

· Registered
Joined
·
167 Posts
One issue I have found in paper mills that are pre 1960's is that many of the motor starters have 480V control voltage, usually just 2 phases from the starter to the push buttons in the control panel. Dangerous and not always marked clearly. On/off controls for pumps sometimes will not shut off when a high resistance ground is present on the phases used. Same for reversing starters.
 

· Registered
Joined
·
16,580 Posts
BT Electric said:
One issue I have found in paper mills that are pre 1960's is that many of the motor starters have 480V control voltage, usually just 2 phases from the starter to the push buttons in the control panel. Dangerous and not always marked clearly. On/off controls for pumps sometimes will not shut off when a high resistance ground is present on the phases used. Same for reversing starters.
And I thought most old paper mills were 575V. May it's a northern thing?
 

· Electron Flow Consultant
Joined
·
3,307 Posts
And I thought most old paper mills were 575V. May it's a northern thing?
They still have quite a bit of 480V controls at one of our sites. We converted about 40 starters to 120V a couple years ago. Changed out CPT's, coils, fusing, and added PLC controls. I think they would have been better off buying new buckets and starters. Of course they had us install I/P's and P/I's to integrate the pneumatics into the DCS.
 