No one has said that 2/3-poles can't be a MWBC, only that that is not the only (or primary) use for them.
Actually I think this would qualify....
A 240V circuit is not a MWBC.
Anytime you only use two phases you are using single phase.
Example: 240V single phase (L1-L2) load from a 120/240V 3ph system = single phase load
208V single phase (L1-L-2) resistive heater from a 208/120V system = single phase load.
I can see where this might get confusing, at least from where I've researched. Feel free to correct me on this manner as I will admit my background is more on residential.
So here goes my thoughts...
On the commercial side of things the term single phase 208v is used to describe the connection utilizing the wild leg on a 240/120-volt 4-wire delta. To my knowledge that is it but please elaborate.
Also, there seems to be, unknowingly to me, a lot water heaters that use this very connection and the nameplate will read 208v single phase.
Moreover, on a commercial 208Y/120-volt 3-phase wye system, there is no 208v single phase, but rather 208v 3-phase.
On the residential side, the term single phase describes the 120/240 single-phase or sometimes referred to as split-phase, supplying homes.
On the down low, it is best to describe breakers in terms of there poles and not the phases they utilize. For example, 1pole, 2pole, 3pole and so on and never use the term 1phase 2phase or 3phase to describe breakers.
That's all I got to offer on that.:thumbup: