Is this a ECO tripping?
Chances are the dip tube is cracked or broken and cold water is bypassed and the units is over heating where the limit is.
if the unit was over pressure or temperature in a unsafe condition the TPSV will open.
If a old tank scale build up can cause this as well but rarely. Usually the efficiency is noticeably reduced.
Chances are the dip tube is cracked or broken and cold water is bypassed and the units is over heating where the limit is.
if the unit was over pressure or temperature in a unsafe condition the TPSV will open.
If a old tank scale build up can cause this as well but rarely. Usually the efficiency is noticeably reduced.