Normal if I saw this I might just turn my back and walk away but this happens to be one of my better customers. This building has been through numerous remodels and at one point a fascia wall was built about 16" in front off this 24X16X4 can above a panel. the pictures could have been better, the camera is in front of the panel pointing up and the white bar you see at the top of the first picture is the top of the door jam entering the electrical closet. there is a stucco wall about 16" in front of the can.
The hackery is strong here. I was called to replace a timeclock with a photocell because the guy in charge of adjusting dusk and dawn isn't doing his job.
What I found was both 110 fixtures and 220v HID fixtures wired off of the TC101... problem you say? no problem, we only switch one leg to the HIDs and the lights go off when when the TC101 opens
It gets better, not only are the loads for the HIDs not on the same breaker, they are not even on the same side of the panel :thumbup:
the Lighting circuit is all being fixed with a contactor and breaker rearrangement but I am worried about the clearance in front of the can.