When using a scope test under load. I compared to the building power. Just make sure to have the scope plugged into the generator power because the neutral or grounds are tied together in the scope
When using a scope test under load. I compared to the building power. Just make sure to have the scope plugged into the generator power because the neutral or grounds are tied together in the scopeBesides checking the voltage and frequency from your multimeter, how could you determine if the generator output is clean. I haven't used an o-scope since trade school, and wouldn't know what to look for, but I do have access to a decent one. It's a 1750 kw genset powered by a cat and just recently when testing it the ats was slow to sync.
First time poster, but long time follower.
Any thoughts?
Good point. Would you just look for some ripple or deviation in the frequency? I assume looking at it line to line rather than line to neutral as the ats is a 3 pole and the neutral is tied to the utility. Or would it be better to test line to neutral?dronai said:When using a scope test under load. I compared to the building power. Just make sure to have the scope plugged into the generator power because the neutral or grounds are tied together in the scope
Unless you isolate the AC scope power, testing line to line will create a short because the ground clip on the probe is tied to ground. You could test line to neutral or line to line with 2 probes and not connect the ground clips though. It's a bit dangerous unless you are sure of what you are doing.Good point. Would you just look for some ripple or deviation in the frequency? I assume looking at it line to line rather than line to neutral as the ats is a 3 pole and the neutral is tied to the utility. Or would it be better to test line to neutral?
fifyI was getting a false reading for HZ on a hand held meter. So I used the scope to check. Some ET members told me to test under load but I didn't listen to them.
fify![]()
Standby idling type. I also checked with my portable Honda at home, and the same result. With my hand held the reading was at 180 HZ, and 60HZ in the wall outlet ?Dronai, was this an idling generator or a inverter type generator?