Someone tried telling me today that you can only run 2 12/2 pieces of Romex through a 3/4" hole drilled through a stud. I said there's no such code. At least I never heard of such a thing but he swears by it. Is there anything that limits the amount of cables through a hole?
 

·
Electrical Simpleton
Joined
·
3,350 Posts
334.80 Ampacity. The ampacity of Types NM, NMC, and
NMS cable shall be determined in accordance with 310.15.
The allowable ampacity shall not exceed that of a 60°C
(140°F) rated conductor. The 90°C (194°F) rating shall be
permitted to be used for ampacity adjustment and correction
calculations, provided the final derated ampacity does not ex-ceed that of a 60°C (140°F) rated conductor. The ampacity of
Types NM, NMC, and NMS cable installed in cable tray shall
be determined in accordance with 392.80(A).
Where more than two NM cables containing two or
more current-carrying conductors are installed, without
maintaining spacing between the cables, through the same
opening in wood framing that is to be sealed with thermal
insulation, caulk, or sealing foam,
the allowable ampacity
of each conductor shall be adjusted in accordance with
Table 310.15(B)(3)(a) and the provisions of 310.15(A)(2),
Exception, shall not apply.
Where more than two NM cables containing two or
more current-carrying conductors are installed in contact
with thermal insulation without maintaining spacing be-tween cables, the allowable ampacity of each conductor
shall be adjusted in accordance with Table 310.15(B)(3)(a)

Pete
 

·
Registered
Joined
·
114 Posts
Not for the width of a stud, that I'm aware of.

For longer distances, I think there is a limit of CCC's, but 1.5" isn't where that starts. :)
 

·
Registered
Joined
·
114 Posts
334.80 Ampacity. The ampacity of Types NM, NMC, and
NMS cable shall be determined in accordance with 310.15.
The allowable ampacity shall not exceed that of a 60°C
(140°F) rated conductor. The 90°C (194°F) rating shall be
permitted to be used for ampacity adjustment and correction
calculations, provided the final derated ampacity does not ex-ceed that of a 60°C (140°F) rated conductor. The ampacity of
Types NM, NMC, and NMS cable installed in cable tray shall
be determined in accordance with 392.80(A).
Where more than two NM cables containing two or
more current-carrying conductors are installed, without
maintaining spacing between the cables, through the same
opening in wood framing that is to be sealed with thermal
insulation, caulk, or sealing foam,
the allowable ampacity
of each conductor shall be adjusted in accordance with
Table 310.15(B)(3)(a) and the provisions of 310.15(A)(2),
Exception, shall not apply.

Where more than two NM cables containing two or
more current-carrying conductors are installed in contact
with thermal insulation without maintaining spacing be-tween cables, the allowable ampacity of each conductor
shall be adjusted in accordance with Table 310.15(B)(3)(a)

Pete
I (somewhat) stand corrected :). Thanks Pete.

Still at 80% you're allowed 4-6 CCC's, so that would be 3, 12-2 Romex cables.

Really, in a 3/4" hole, without stuffing it full, I doubt you could get many more than 3 anyway.
 

·
Registered
Joined
·
365 Posts
I (somewhat) stand corrected :). Thanks Pete.

Still at 80% you're allowed 4-6 CCC's, so that would be 3, 12-2 Romex cables.

Really, in a 3/4" hole, without stuffing it full, I doubt you could get many more than 3 anyway.
You can run 4- 12/2's or 4- 14/2's. By derating the #12 would be at 30 amp in the 90 deg column. 8 ccc @ 70% would be 21 amps so you are good. Same with #14 8 ccc @70 of 25 amps would be 17.5 on a 15 amp ocd.
 

·
Registered
Joined
·
57 Posts
You can run 4- 12/2's or 4- 14/2's. By derating the #12 would be at 30 amp in the 90 deg column. 8 ccc @ 70% would be 21 amps so you are good. Same with #14 8 ccc @70 of 25 amps would be 17.5 on a 15 amp ocd.
I thought you were required to use the 60 deg column for nm?
 

·
Registered
Joined
·
365 Posts
I thought you were required to use the 60 deg column for nm?
You are. Read the entire code article Pete posted. You can use the 90 deg. column for derating but the ampacities of the wire must not be below the rating in the 60 deg. column. So with derating for 8 ccc #12 wire has an ampacity of 21 amp. So it is above the max ocp of 20 amps. Same with # 14. 17.5 ampacity of the wire on a 15 amp breaker.
 

·
Registered
Joined
·
57 Posts
Duh, yes I plainly see it. I'm sure I knew this at one time. Memory is not as good as it once was.
 

·
Registered
Joined
·
809 Posts
Weve always ran 4 NM through a 7/8" hole. I never understood that code when we are allowed to put all our hrs through a 2 1/2" pvc sleeve
 

·
fertilizer distrubuter
Joined
·
1,250 Posts
Sometimes the St. Louis area inspectors will get you on 110.12 if you run more than one per hole.

Dont get me started on how stupid this is.
 

·
corn-fused
Joined
·
4,769 Posts
the way im reading petes code quote is 'IF THE HOLE WILL BE SEALED' but sorry ,too tired to look it up.:001_huh:
 