I work in a plant that was built in the 50's. They have since added a bunch of additions and sprawled out everywhere. I was wondering if there is a generic point where you just go "yup 2000amps for you because you'll probably need it in 40 years" or if it's more common to add another service on an addition.

Thanks yall I never work on services so I really have no idea.
 

· Chief Flunky
Field Service Engineer
Joined
·
4,174 Posts
I work in a plant that was built in the 50's. They have since added a bunch of additions and sprawled out everywhere. I was wondering if there is a generic point where you just go "yup 2000amps for you because you'll probably need it in 40 years" or if it's more common to add another service on an addition.

Thanks yall I never work on services so I really have no idea.
You have to “what if” about reasonable size. What would it look like in say 25 years…how would it grow. How does that compare to today? Maybe a “good/better/best” scenario. Then cost them out (budgetary) and present options to the bean counters. This is usually an engineering question.

Same thing when you design the equipment. Maybe you oversized some things or leave space. Quite often what happens with large expansions is you may plan for your entire system to become a substation to a larger sun at a later time.
 

· Senile Member
I make all the electrons line up for their Flu shots
Joined
·
37,481 Posts
Hire an EE to figure it all out.. Better yet, have the building owner hire an EE to figure it all out. And experienced and shall I dare say it , well aged experienced EE...............
 

· Registered
Commercial and Industrial Service
Joined
·
40 Posts
Discussion Starter · #5 ·
There are too many variables in your question to give you an answer of any value to you.
It's ok. The other answers are sufficient and make sense. It was just a general question!

Thanks guys. I figured it would probably be an engineer's job. I also figured a plant would never want to shut down for a service upgrade either so that would drive them to go big.
 

· Chief Flunky
Field Service Engineer
Joined
·
4,174 Posts
It's ok. The other answers are sufficient and make sense. It was just a general question!

Thanks guys. I figured it would probably be an engineer's job. I also figured a plant would never want to shut down for a service upgrade either so that would drive them to go big.
As an engineer you start with the loads, both total and the larger ones. Also a good idea of layout, existing or planned. This step generally involves working with process engineers or sometimes equipment manufacturers. This gets into the soft side if engineering. There are some “guidelines”. For instance if a chemical engineer sizes a pump, plan on a +/-50% error in their calculations. Look at the overall design and leave between 10 and 50% extra capacity, again depending on how reliable the design data is. Be prepared to pivot multiple times. Typically they will want to put the electrical gear in a stupid and bad spot as well as change their minds twice a week. It helps to have a very high tolerance for a lack of commitment and people coming up with all kinds of craziness. You have to learn how to adapt quickly. Don’t get too hung up on perfecting any design. Flexible, modular designs are key. But as you move into construction planning the designers will want to tinker constantly (that’s what they do). That’s when you need to be firm in moving forward.

Once you get through a rough design (roughly a load list), there are certain “limits” that you should respect. For instance above roughly 200-250 HP, 208 or 230 V becomes more difficult to support. With 480 of 600 that increases to 500 HP with starters, 1000 HP with drives although I’ve had issues at 700+ HP drives. That pushes you into MV. Line losses may also be a determining factor. For total power I try to split out another transformer at 1000 kVA. Why so small? For one thing arc flash and maintaining under 40 cal in some cases and 8 cals for “every day” is easily achieved. For another we can use cheap panelboards and ILines and reduce the amount and cost of wiring to the loads. Similarly at 4160 things become a lot more challenging above about 5000 HP per load and 10 MVA overall, pushing you into the 15 kV class (12,470 or 13,500) or possibly jumping to 35,400. At this point for practical reasons you sort of have to adopt the local utility distribution designs. If you don’t and there are issues on their end, getting back online can be a long drawn out process.

You CAN buy much higher rated equipment but there are consequences. When you jump from 35 kA ratings to 65 kA ratings on breakers for instance the prices triple not just at the switchgear but on every control panel and most downstream devices. Similarly at MV staying under 10 kA short circuit and under 500 A loads (1000 A at most) is reasonably priced. Costs explode as you go above those thresholds. In years past it was very easy to figure this out because we had printed catalogs where you could look right down the Colin. Today getting pricing is like pulling teeth.

At one time all these general design guidelines were published in the IEEE Red Book for industrial plants. Similar ones are available for commercial. Now IEEE is finally revising them after decades of collecting dust but the new versions are scattered.

I tend to just do everything in HP and kVA. It’s just easier. With motors use 5x the largest plus the total HP and assume 1 kVA=1 HP (85% efficiency, a reasonable fudge factor). With under 5 loads you may want to use VD estimates and don’t use the 5x number so it doesn’t blow up sizing. This is where soft starts make good economic sense.

I’m saying this much because it gives you an idea of what goes into the decision making because it is very different from just calculating cable ampacity or making stamped drawings for permitting.

You need experience (10+ years) to be successful in herding cats and dealing with people that struggle with decision making. You sort of have to be both coach and human calculator. You have to recognize that this is all a “process” with an overall design procedure. It often drives field guys that are results oriented crazy. It takes training in coaching and project management and experience to do this.
 

· Hackenschmidt
Joined
·
14,547 Posts
It's like anything else. If you know what you'll need, you can plan for it. If you have an educated guess and a number of likely options, you can plan flexibility to adapt as you grow when you see what the future holds. Or, you can just pull numbers out of your ass and hope for the best, push it as far as possible and then some, and do what you have to to change when the time comes.
 

· Registered
Joined
·
7,015 Posts
Call downtown and see what they say at the permitting department. In the City I live in, you cant do a job of this size without an architect or EE stamping off a set of prints.

The city set our limit on non-residential projects to $35,000. Everything over that number needs a set of prints & stamps, everything under that limit the contractor can pull a stand alone permit and design it however they want in the field. Assuming its code compliant of course.
 

· Registered
Power distribution and controls
Joined
·
3,173 Posts
A lot to consider. I would start what is my incoming voltage? If I ask for a 4000 amp service will the POCO allow me to have it? What is the power factor now? What was it a year ago? Contact the POCO for that information.

I worked for a company that wanted to put in a dyno for testing motors that we rebuilt in the motor shop these motors were 5kv. POCO said no to a 3000 and up service. So the people in charge bought off on a 2000 amp service as cheap as they could purchase. Then they bought a 480-5kv pad mounted transformer to buck up the voltage. Once every thing was installed they quickly found out that the over current device on the main would not allow the motors to start even with a MotorTronics VFD. So some genius came up with the idea of a push button on the CT's to override the starting current. I was asked to get involved and declined. Key word was asked. I went to my boss an intelligent guy and asked at lunch away from the property "Do you think this is a good idea?" He indicated that he did not.
So when I left the company every time they wanted to test a motor they pushed a button on the side of the control cabinet which shunted the CT's. At least it was inside and away from the service.
The company tried to get a 5kv service and was denied. Because of the cost to rebuild the over head distribution lines and the new transformers need at the substation.
This was a light commercial area not heavy industrial the feeders were not there on the POCO side.

Gather information and then sit down with management about new loads and operations.

Be thankful that your company is growing.
 

· Registered
Design, build, repair panels. Install industrial electrical.
Joined
·
797 Posts
I work in a plant that was built in the 50's. They have since added a bunch of additions and sprawled out everywhere. I was wondering if there is a generic point where you just go "yup 2000amps for you because you'll probably need it in 40 years" or if it's more common to add another service on an addition.

Thanks yall I never work on services so I really have no idea.
Everyone else has already given you the general 'not enough info' answer, which is fair. I will point out that it's a lot cheaper to run one 2000A service once than to run two 1000A services at different times. If you have to run a service anyway, then get a range of quotes for substations etc. so that you have a few numbers to pick from, and make sure you include the small sizes so that whoever is making the decision can get a feel for the ramifications if they guess too small.
 

· Registered
Electrical contractor 37 years. Electrical inspector 2 years
Joined
·
4,373 Posts
Before 2020 you could install a main lug service panel with six disconnects. Now you need separate compartments for each disconnect......
What we did on several jobs in the past is install a 2000 amp MLO switchgear with 5 - 4 inch PVC conduits to the transformer vault. We only installed 2 sets of 500kcmls and an 800 amp I Line breaker to start. Many years later we pulled additional sets of 500kcmls and installed additional breakers as needed. Back then PVC was cheap . Now the equipment is much larger and PVC is no longer cheap. I would not do this today.
 

· Registered
Design, build, repair panels. Install industrial electrical.
Joined
·
797 Posts
Before 2020 you could install a main lug service panel with six disconnects. Now you need separate compartments for each disconnect......
What we did on several jobs in the past is install a 2000 amp MLO switchgear with 5 - 4 inch PVC conduits to the transformer vault. We only installed 2 sets of 500kcmls and an 800 amp I Line breaker to start. Many years later we pulled additional sets of 500kcmls and installed additional breakers as needed. Back then PVC was cheap . Now the equipment is much larger and PVC is no longer cheap. I would not do this today.
I've been in situation like that were we were able to pull more conductors through unused conduits, but that usually only occurs in situations where several services are fed from one sub-station. Like a commercial or industrial situation where a large building has a number of tenants which could be a warehouse needing 500A or a plastics extrusion place needing 2000A, and you don't know what you're going to get until they move in, so the building managers can shuffle the shares of electricity around to make it all work. If you need to add a new service to an existing building with a single tenant then you're going to run conduit to handle whatever the substation is capable of supplying. If you replace the substation later with a larger one then adding more conduit will be the least of your worries.
You point is well taken, though. Future-proofing decisions is important. I try to run conduit and conductors so that I will have some wiggle-room if I'm up-sizing something in the future. Doesn't always work, of course, but it's worth trying. The price difference between, say, #14 and #12 is pretty small potatoes in the grand scheme of things, and if it saves your bacon even one in 10 times it's worth it.
 

· Registered
Commercial and Industrial Service
Joined
·
40 Posts
Discussion Starter · #13 ·
Some of this is way over my head but I'm looking it up as you guys respond so thanks. @paulengr that's extremely useful to know what the limits are for 40 cal occasionally and 8 cal everyday as well as when prices triple on equipment.

I did clean switch gear once in a plant that had one substation on each end of the building and could only run at night due to power demand. But as far as I know the dairy plant I'm at has the same original ungrounded delta service. Not sure the size I'll have to check Monday.

@MHElectric think my area has something similar for when you need stamped prints but I should find out.
 

· Chief Flunky
Field Service Engineer
Joined
·
4,174 Posts
A lot to consider. I would start what is my incoming voltage? If I ask for a 4000 amp service will the POCO allow me to have it? What is the power factor now? What was it a year ago? Contact the POCO for that information.

I worked for a company that wanted to put in a dyno for testing motors that we rebuilt in the motor shop these motors were 5kv. POCO said no to a 3000 and up service. So the people in charge bought off on a 2000 amp service as cheap as they could purchase. Then they bought a 480-5kv pad mounted transformer to buck up the voltage. Once every thing was installed they quickly found out that the over current device on the main would not allow the motors to start even with a MotorTronics VFD. So some genius came up with the idea of a push button on the CT's to override the starting current. I was asked to get involved and declined. Key word was asked. I went to my boss an intelligent guy and asked at lunch away from the property "Do you think this is a good idea?" He indicated that he did not.
So when I left the company every time they wanted to test a motor they pushed a button on the side of the control cabinet which shunted the CT's. At least it was inside and away from the service.
The company tried to get a 5kv service and was denied. Because of the cost to rebuild the over head distribution lines and the new transformers need at the substation.
This was a light commercial area not heavy industrial the feeders were not there on the POCO side.

Gather information and then sit down with management about new loads and operations.

Be thankful that your company is growing.
I really wouldn’t panic over the CT thing. This is a common technique. ANSI 50/51 relays have a curve designed to protect wiring. It does not work well with any kind of reactive loads. That’s why we use either motor fuses or instantaneous only breakers (with current limiting) and overload relays. It’s common to block CTs for transformers and motors when relays are sized too closely to them or you have one very big motor.
 

· Registered
Electrical contractor 37 years. Electrical inspector 2 years
Joined
·
4,373 Posts
Just farmer engineer it. Carefully calculate present loads, future growth by using past to present growth as precedent, then double the number just to be sure.
That sounds like the old US School of Hard Knocks method. Over engineer everything so it lasts and you can expand. Look at the old 1/2 ton pick up trucks from the 1950s and 1960s, they could hold a ton of weight intermittently without any problems. Today if you put 1500 pounds in a 1/2 ton you will pop the springs. I look at stuff made to NEMA standards. It lasts forever, almost. Then look at ICC made stuff. It is engineered just so and no wiggle room, it also does not last as long and cannot take abuse.
 

· Registered
Electrical contractor 37 years. Electrical inspector 2 years
Joined
·
4,373 Posts
I really wouldn’t panic over the CT thing. This is a common technique. ANSI 50/51 relays have a curve designed to protect wiring. It does not work well with any kind of reactive loads. That’s why we use either motor fuses or instantaneous only breakers (with current limiting) and overload relays. It’s common to block CTs for transformers and motors when relays are sized too closely to them or you have one very big motor.
Paul, you have to dumb down your answers. Your experience and knowledge are way over my head at times. I have to read it several times to understand what you are saying. :). NY does not push us electricians or anything that is important. Guys on ET talk about breaker curves and faults currents or what ever and most electricians here know very little about it. Last week I listened to a Bussman fuse presentation about fault currents, curves, and coordination and out of about 30 electricians only 3 or 4 knew anything about it. But we are trained in sexual harassment and gender identity.
 