· Registered
Electrical contractor 37 years. Electrical inspector 2 years
Joined
·
4,373 Posts
Floating neutral just means it is not bonded to the ground/frame. You can still have 3-wire.
As was mentioned, the OP is trying to run a 120V genny to a 240V TS. The adapter is creating a short. It doesn't matter if there is a load or not because the short is happening when the adapter is plugged in.
NoBot posted the Gen specifications and I see what you are saying. 120 volts only. Definitely not an electrician. Too many cheapo things on the market today. I am use to generators 5000 watts and below to have a bonded neutral and above 5000 watts to have a floating neutral. Hence 3 wire and 4 wire.
 

· Moderator
Estwing magic
Joined
·
28,212 Posts
JohnnyVV, are you an electrical contractor?

 

· Registered
Industrial Control & Automation
Joined
·
48 Posts
These reliance transfer switches are different than the typical ones. It’s like having 10 separate transfer switches, one for each circuit. They can not run off a 120 volt generator with an adapter.

Difficult to have them pass inspection in Canada as well.

The OP most likely installed it incorrectly, without inspection and is not an electrician.
I am not talking about the switch itself. I am talking about the adapter.
 

· Registered
Joined
·
187 Posts
I would check the bridge adapter for proper connections.
My thought as well. If the generator goes into overload with all the breakers turned off, then either the adapter or the transfer switch itself is creating a short circuit. Should be easy enough to figure out which by connecting the adapter but not the transfer switch. Always seems to me to be hinky connecting a 120V generator to a 120/240V transfer switch anyway - if the transfer switch has 120/240V capability, then it does not belong on a 120V generator - but I'm not familiar with that transfer switch.
 

· Registered
Joined
·
2 Posts
Not sure, but are you running extension cord that goes to the four prong box on a 120v outlet on the generator instead of the 240 outlet. It has to be in the 240 outlet on the generator, even if you are not running any double poles on the transfer switch you still need both sides of the power coming from the genrator otherwise you are massively overloading it.

4000 watt generator only puts out 2000 watts through the 120v outlets.

Unless I am mistaken, 120/240 does not mean you can supply with a 120 volt power source.
 

· Registered
Joined
·
187 Posts
contractor?

But not an electrical contractor
I dunno, there are still plenty of places where resi contracting in particular have pretty much zero requirements. A friend asked me to look at the sump pump wiring because his electrician told him his brand new sump pump had a short and it was at the bottom of 480 feet of rigid CPVC pipe. Turns out his electrician was totally illiterate and after forty+ years of wiring houses could not distinguish between "LINE" and "LOAD". Thus he had wired a lightning arrester rotated physically 90 degrees so that "L1" shorted directed to "L2" once the breaker was thrown. His electrician was stymied and decided the pump had a short to explain the immediate and quite energetic tripping when the breaker was engaged. (Dude's "meter" was a piece of 2x4 with a 120V doorbell nailed to it - touch wires to the two nails with leads wrapped around them and if the doorbell rings, there's voltage. Unfortunately doorbells don't come with continuity or resistance functions . . .) Point being that Johnny actually might be an electrical contractor, but without the amount of knowledge that you possess and consider to be the minimum to be an electrician, or at least an electrical contractor. But he might be competent within his own area of work and experience. He seemed to me to have an understanding reasonably commensurate with a residential electrical contractor who's not worked commercial or gone through a Union apprenticeship program.

Either way, it does highlight the dangers inherent within a professional technical forum. A lot of people feel it's just snobbery that electricians only help other electricians. But if one claims to be an electrician, there's a vast amount of knowledge that electricians assume one knows, and with electricity, what you don't know, but don't know that you don't know, can kill you. Hopefully Johnny is an electrical contractor and knows safety, he's just run into something outside of his own knowledge and experience.
 

· Light Bender
plumber
Joined
·
7,650 Posts
I dunno, there are still plenty of places where resi contracting in particular have pretty much zero requirements. A friend asked me to look at the sump pump wiring because his electrician told him his brand new sump pump had a short and it was at the bottom of 480 feet of rigid CPVC pipe. Turns out his electrician was totally illiterate and after forty+ years of wiring houses could not distinguish between "LINE" and "LOAD". Thus he had wired a lightning arrester rotated physically 90 degrees so that "L1" shorted directed to "L2" once the breaker was thrown. His electrician was stymied and decided the pump had a short to explain the immediate and quite energetic tripping when the breaker was engaged. (Dude's "meter" was a piece of 2x4 with a 120V doorbell nailed to it - touch wires to the two nails with leads wrapped around them and if the doorbell rings, there's voltage. Unfortunately doorbells don't come with continuity or resistance functions . . .) Point being that Johnny actually might be an electrical contractor, but without the amount of knowledge that you possess and consider to be the minimum to be an electrician, or at least an electrical contractor. But he might be competent within his own area of work and experience. He seemed to me to have an understanding reasonably commensurate with a residential electrical contractor who's not worked commercial or gone through a Union apprenticeship program.

Either way, it does highlight the dangers inherent within a professional technical forum. A lot of people feel it's just snobbery that electricians only help other electricians. But if one claims to be an electrician, there's a vast amount of knowledge that electricians assume one knows, and with electricity, what you don't know, but don't know that you don't know, can kill you. Hopefully Johnny is an electrical contractor and knows safety, he's just run into something outside of his own knowledge and experience.
Great story, but the OP is from Canada were there are mandatory requirements to do electrical contracting and electrical work. Also, considering the OP has not come back and has not answered my question or the same question from a moderator, I'd guess that no, he is not an electrical contractor
 

· Registered
Joined
·
187 Posts
Great story, but the OP is from Canada were there are mandatory requirements to do electrical contracting and electrical work. Also, considering the OP has not come back and has not answered my question or the same question from a moderator, I'd guess that no, he is not an electrical contractor
Noted.

Ought to be mandatory requirements everywhere to do electrical work on other people's property. Including basic literacy.
 