I just failed electrical inspection because my #6 ground wire was taped green and was told it needs to be solid green insulation. After reading 200.6 I see that the grounded conductor (Neutral) needs to have outer sheath permanently marked. Is he correct?
1 - 20 of 24 Posts
I just failed electrical inspection because my #6 ground wire was taped green and was told it needs to be solid green insulation. After reading 200.6 I see that the grounded conductor (Neutral) needs to have outer sheath permanently marked. Is he correct?
What are you wiring?
Are you running cable or individual conductors?

Edit: The ground (EGC) and neutral are two separate conductors.
Think I am wrong it is the EGC and 250.119
Think I am wrong it is the EGC and 250.119

It needs to be larger than #6, so the inspector is correct.
Little-Lectric said:
It needs to be larger than #6, so the inspector is correct.
Yes he is stupid mistake !!!
  • Like
Reactions: 1
Take a utility knife and strip off the insulation. Inspector wont know.

If I was him I would let it slide, but they always go after the little things:rolleyes:
meadow said:
Take a utility knife and strip off the insulation. Inspector wont know. If I was him I would let it slide, but they always go after the little things:rolleyes:
I was thinking of that or even but splicing both ends :) he also got me for not bringing EGC through both transfer switches continuously
I was thinking of that or even but splicing both ends :) he also got me for not bringing EGC through both transfer switches continuously
:laughing: As long as its bonded who cares. Sounds like an anul inspector. What he doesn't know wont hurt:whistling2:
I was thinking of that or even but splicing both ends :) he also got me for not bringing EGC through both transfer switches continuously
EGC? Grounding Electrode Conductor? Did he give you a code ref, if not I don't respond.
backstay said:
EGC? Grounding Electrode Conductor? Did he give you a code ref, if not I don't respond.
EGC and GEC have different rules.
A GEC cant have any splices unless its an irreversible weld/crimp... in lay mans terms that means a continuous wire from panel to rode/water bond.
A GEC cant have any splices unless its an irreversible weld/crimp... in lay mans terms that means a continuous wire from panel to rode/water bond.
I splice them with a crimp a lot. Take a situation where the GEC is sized correctly when I do a panel change, but it only has one rod. I set another rod and crimp a wire to the original GEC.
I splice them with a crimp a lot. Take a situation where the GEC is sized correctly when I do a panel change, but it only has one rod. I set another rod and crimp a wire to the original GEC.

Not saying you cant but in a new install its easier to just avoid it as much as you can. Kind of like splices in a panel.

And not all crimps are rated as irreversible, correct? Ive always thought all were rated like that but I don't know.
GEC's can be spliced on a terminal bar. 250.64 C 2
  • Like
Reactions: 1
It needs to be larger than #6, so the inspector is correct.
# 4 for that....you can run #6 for your water bonds...
Not saying you cant but in a new install its easier to just avoid it as much as you can. Kind of like splices in a panel.

And not all crimps are rated as irreversible, correct? Ive always thought all were rated like that but I don't know.
I use these.
  • E-Z-Ground® connectors are designed for direct burial and offer a safe, efficient alternative to exothermic welding products.


http://www.tnb.com/ps/fulltilt/index.cgi?part=BC202

See less See more
  • Like
Reactions: 1
A GEC cant have any splices unless its an irreversible weld/crimp... in lay mans terms that means a continuous wire from panel to rode/water bond.
There's more to it.

The GEC would be the conductor going from the panel to the water pipe. But you can splice on another conductor to go from there to the rods, and that does not have to be irreversible because it's a bonding jumper and not a GEC.

The same with 2 panels, you can splice onto the GEC going into one panel with a non-irreversible splice to bring the bonding jumper into the second panel.
  • Like
Reactions: 1
There's more to it.

The GEC would be the conductor going from the panel to the water pipe. But you can splice on another conductor to go from there to the rods, and that does not have to be irreversible because it's a bonding jumper and not a GEC.

The same with 2 panels, you can splice onto the GEC going into one panel with a non-irreversible splice to bring the bonding jumper into the second panel.
And if the water pipe is plastic? Then I can skip the GEC?
And if the water pipe is plastic? Then I can skip the GEC?
No, then the GEC would be the conductor going to the ground rods or whatever other type of electrode you were using.




See less See more