I frequently install Infratech electric patio heaters. Usually I install with 240V switches or Infratech relay panels controlled by smart switches.
They make a single or dual contactor panel that can be controlled by switches on a separate circuit or use smart switches to control the heaters.
They specify a maximum wattage of 6KW for each contactor relay. If I use 2 - 240V 4KW heaters (1 on each contactor) with 10awg wire to each heater, they specify a 42Amp main feed for the contacotr panel, however there is no individual overcurrent protection for each 4KW heater wiring. I have short circuit & ground fault protection provided by the 42A main feed circuit breaker.
How is this safe or approved to use in this way?
They make a single or dual contactor panel that can be controlled by switches on a separate circuit or use smart switches to control the heaters.
They specify a maximum wattage of 6KW for each contactor relay. If I use 2 - 240V 4KW heaters (1 on each contactor) with 10awg wire to each heater, they specify a 42Amp main feed for the contacotr panel, however there is no individual overcurrent protection for each 4KW heater wiring. I have short circuit & ground fault protection provided by the 42A main feed circuit breaker.