Hi Folks, just wondering if I could get some opinions on a job i'm planning.
I need to install a new 125A 3P fused switch to supply a new electric furnace.
The existing equipment consists of a 200A 3P sub-board fed from a 600/208 transformer fed from the building 600v , the 200A fuses being on the line side of the transformer.
I was thinking of swapping out the lugs in the sub-board for 2 conductor types and tapping my fuse switch from there, would this be acceptable from a code point of view?
Any input is appreciated
I need to install a new 125A 3P fused switch to supply a new electric furnace.
The existing equipment consists of a 200A 3P sub-board fed from a 600/208 transformer fed from the building 600v , the 200A fuses being on the line side of the transformer.
I was thinking of swapping out the lugs in the sub-board for 2 conductor types and tapping my fuse switch from there, would this be acceptable from a code point of view?
Any input is appreciated