Hi all,
In a private dwelling in Spain, I have a situation where the feed from the street comes in as a dual 136Vac feed (2 phases) which are combined at the primary switchboard to give a 240Vac supply to the household.
The result of this is that you have a "floating" earth, where your measurements between N & L is 240Vac, yet between each N or L with Earth is 136Vac.
This is due to the old Spanish supplies, which are still going through the transition/upgrade to the current standard of 400/230Vac (3phase/single phase) setup.
Although for your standard domestics this installation is acceptable, for more sensitive devices, as well as any PAT testing, this causes issues.
To correct the setup, I intend to put inline an isolating transformer to achieve 2 targets.
Rectify the feed to the sub-board with a true L-N-E installation where N-E are bounded.
And to separate out the RCP of the 2 boards (so that a leakage in the "rectified" zone will not trip the main RCP at the residence primary board.
My request here is, that someone cast a second eye on the setup to confirm my thoughts on the wiring.
The primary board has the 2 phases wired as an N-L combination, with earth unbound. An RCP across the N-L line.
The primary winding on the transformer is connected to each 136Vac phase, with the secondary winding thus giving 240Vac between N-L.
On the second winding of the transformer, the intention is to bind N to E and feed the sub-board
and to have an RCP on the sub-board for leakage protection of this zone.
Any comments? Any hidden issues that I am missing?
Thank you,
Tim.
In a private dwelling in Spain, I have a situation where the feed from the street comes in as a dual 136Vac feed (2 phases) which are combined at the primary switchboard to give a 240Vac supply to the household.
The result of this is that you have a "floating" earth, where your measurements between N & L is 240Vac, yet between each N or L with Earth is 136Vac.
This is due to the old Spanish supplies, which are still going through the transition/upgrade to the current standard of 400/230Vac (3phase/single phase) setup.
Although for your standard domestics this installation is acceptable, for more sensitive devices, as well as any PAT testing, this causes issues.
To correct the setup, I intend to put inline an isolating transformer to achieve 2 targets.
Rectify the feed to the sub-board with a true L-N-E installation where N-E are bounded.
And to separate out the RCP of the 2 boards (so that a leakage in the "rectified" zone will not trip the main RCP at the residence primary board.
My request here is, that someone cast a second eye on the setup to confirm my thoughts on the wiring.
The primary board has the 2 phases wired as an N-L combination, with earth unbound. An RCP across the N-L line.
The primary winding on the transformer is connected to each 136Vac phase, with the secondary winding thus giving 240Vac between N-L.
On the second winding of the transformer, the intention is to bind N to E and feed the sub-board
and to have an RCP on the sub-board for leakage protection of this zone.
Any comments? Any hidden issues that I am missing?
Thank you,
Tim.