Autotransformers are not isolating.Technically all transformer's are isolating,
ANDNow there are some applications of isolating transformers that require the secondary to not be grounded like in some special medical applications.
Usually the primary is grounded,whilst not always at the tranny,So to end this, An isolated transformer is generally a normal inductive transformer (not an auto transformer), and it has nothing to do with the grounding of the P or the S ?
Am i right ?
as it could be the instalation that is grounded, (bonded).
And usually the secondary is NOT grounded.
This means that if you touch the secondary hot and ground you will not receive a shock.
This is why they are used to repair televisions and such by repair personnel.
They remove the neutral ground bond.
Are you saying that an Isolated transformer is one that is ungrounded on the secondary ?
This brings us back to the beginning
The primary distribution system is a grounded system
the secondary is almost always grounded except in certain circumstances.
Unless someone can tell me different, as I am not the smartest person here, YES.That's what i was thinking about,
Just to be sure on this, does the name (isolated transformer) apply to any induction transformer that is only connected via induction ?
Regardless of it being a transformer or a generator in most cases the NEC will require the grounded conductors to be directly connected to each other via the grounding electrodes.Bob
Years ago a manufacture of Motor generator came out with a motor to a belt driven generator, they claimed this was true isolation. The design called for PVC pipe and a separate electrode system, with an isolated raised floor.
Correct but this design did not call for that, in testing we proved that they lost their attempt at 100% isolation, somewhere they had an accidental connection to the base building groundRegardless of it being a transformer or a generator in most cases the NEC will require the grounded conductors to be directly connected to each other via the grounding electrodes.
The part about this that is wrong is the use of the term "inductive" as somehow being the opposite of an autotransformer. An autotransformer is inductive too.So to end this, An isolated transformer is generally a normal inductive transformer (not an auto transformer), and it has nothing to do with the grounding of the P or the S ?
Am i right ?