Probably wants to do the bulk of the work while the weather is good.So... if you don't have the disconnect or the generator there to land the conductors in, why are you pulling them. Sounds to me like a good way to get the copper stolen.
Sent from my SM-S908U using Tapatalk
Since most here use Aluminum I just assumed aluminum. Plus the standard stocking size wire is 250, 350, 500 kcmls. The 300, 400, 600 are special orders if you can get them. At least around here. I have a 600 amp breaker on the shelf and I will check the size. Maybe it is only 400 kcmls, I know it is larger than 350.Not quite true.
Square D standards:
Loading…
www.usbreaker.com
Two holes, 400 MCM max, Cu only.
A common private labeled breaker:
Loading…
www.lselectricamerica.com
Page 99 states lug holes (I think 2) are for 3/0 to 500 MCM aluminum, or 3/0 to 350 MCM copper. So 500 MCM copper probably fits but it’s not rated for it.
ABB/Hitachi/GE:
ABB TCAL63 :: Breaker Molded Case, Lug Kit, 2 x 4/0-350MCM CU, 2 x 300-500MCM, AL :: Gexpro
Breaker, Lug Kit, Front Connection, 2 x 4/0 AWG - 350 MCM CU, 2 x 300 - 500 MCM AL, Cat #: TCAL63, Mfr: ABBwww.gexpro.com
4/0-350 copper, 300-500 aluminum.
So I’m curious, which brand of breaker has two 500 MCM lugs at 600 A? None of the common ones do.
Siemens.Not quite true.
Square D standards:
Loading…
www.usbreaker.com
Two holes, 400 MCM max, Cu only.
A common private labeled breaker:
Loading…
www.lselectricamerica.com
Page 99 states lug holes (I think 2) are for 3/0 to 500 MCM aluminum, or 3/0 to 350 MCM copper. So 500 MCM copper probably fits but it’s not rated for it.
ABB/Hitachi/GE:
ABB TCAL63 :: Breaker Molded Case, Lug Kit, 2 x 4/0-350MCM CU, 2 x 300-500MCM, AL :: Gexpro
Breaker, Lug Kit, Front Connection, 2 x 4/0 AWG - 350 MCM CU, 2 x 300 - 500 MCM AL, Cat #: TCAL63, Mfr: ABBwww.gexpro.com
4/0-350 copper, 300-500 aluminum.
So I’m curious, which brand of breaker has two 500 MCM lugs at 600 A? None of the common ones do.
Lugs TC2J6500Siemens.
I sometimes get confused in the conversations here because what is common to some parts of the country is not available or uncommon here and visa versa. Our utility company has there own quirky rules and NY State is far behind with the NEC. Licensing is a joke. Inspections are a joke. Contracting is a joke.3/0 to 500 MCM COPPER ONLY, 2 holes.
For some bizarre reason 300 is common around here. I hate it. I don’t carry lugs for it or any of the other odd sizes but we do cover Flex and coarse strand. We don’t cover DLO either…just not much call for it.
Easy to get around the Cu only. Ilsco makes all kinds of crimped pigtail or pin adapters.