Kohler 100kw 240/120v gen lug size+ dual lugs?

1003 23
Hi all ,
Has anyone hooked up a Kohler 100kw 1/0 240/120v generator before ? I can't get an answer from Kohler on the wire range sizes for the lugs ( ex... 4/0- 500mcm ) . Also I need to know if the gen comes with dual lugs for each phase to allow for parallel feeders . I'm running 125' away from house to gen local . It's Like pulling teeth to get answers unfortunately from Kohler. I've tried for weeks . Any help appreciated. Thanks
1 - 5 of 5 Posts

· Registered
Joined
·
14 Posts
Discussion Starter · #5 ·
Thanks for the quick reply. The supplier finally told me the built in breaker is 600amp . Where would I order a dual lug setup from? Kohler ? . The gen doesn't come in till January but the rough in has to be done next week . I have to pull the feeders next week as well . Right now I'm figuring parallel sets of 350 mcm copper . Good for I think roughly 620 Amps . That should cover the 100% of OC .
 

· Registered
Joined
·
14 Posts
Discussion Starter · #7 ·
The largest generator I've wired is a 48 kw 200 amp unit . So this is new territory . And yes I've ordered a 600 amp rated safety switch ( Siemens) ...due in February lol.
 

· Registered
Joined
·
14 Posts
Discussion Starter · #9 ·
So... if you don't have the disconnect or the generator there to land the conductors in, why are you pulling them. Sounds to me like a good way to get the copper stolen.

Sent from my SM-S908U using Tapatalk
Builder is trenching next week . We have the template for rough in . The pvc has to go under a huge patio that's being installed in 10 days . It's a 10,000 sq ft home . Unfortunately the RI has to go in now .
 