Discussion Starter · #1 ·
Hello all: I have a 12/3 run of about 60' partly indoors and partly in a PVC conduit. Problem: there is a short from ground to neutral. Question: How to locate the short: Most of the equipment to locate cables and shorts is very costly. Any way to deduct the distance from the end to the short? Kind Regards, Jon
 

· Registered
Joined
·
1,014 Posts
Hello all: I have a 12/3 run of about 60' partly indoors and partly in a PVC conduit. Problem: there is a short from ground to neutral. Question: How to locate the short: Most of the equipment to locate cables and shorts is very costly. Any way to deduct the distance from the end to the short? Kind Regards, Jon
If its that short of a run in pipe just replace the wire.
 

· Registered
Joined
·
20 Posts
there is a short from ground to neutral.
get rid of the arc-fault breaker and call it a day.:thumbsup: lol

I would use a locator that our company has...but I have no idea what those things cost to buy or rent...

I agree with what others have said, get rid of it and run a new romex to the box that the PVC is connected to, and from there pull 12 awg thwn.
 

· Registered
Joined
·
16 Posts
Discussion Starter · #13 ·
more info, one solution

Hello all: The conduit is PVC 3/4" SCH 40 electrical, a total run of 75' in several sections. There is no GFI and I am testing directly at the wire ends disconnected from the connectors and system. It was installed poorly, with many sharp bends and a U turn. No junction boxes or pull elbows to access it. It will be very hard to easily pull a new wire. If I know the fault location even approximately, I can localize the area and save time. One solution may be a milliohm meter, measure the loop resistance at each of the ends and calculate the resistance, assuming the fault is a dead short. I am open to your further ideas! With Kind Regards, Jon
 

· Registered
Joined
·
2,655 Posts
One solution may be a milliohm meter, measure the loop resistance at each of the ends and calculate the resistance, assuming the fault is a dead short.
Good thinking, but the chances of a zero ohm short is pushing it. Actually though, it wouldn't have to be a perfect short, but a consistent short that you could add to your calculations on each end. Don't move the wires around too much while you are doing this. :laughing:
 

· Registered
Joined
·
16 Posts
Discussion Starter · #16 ·
2 solutions

Hello all: Being an electrical engineer, I thought of 2 tests: #1 4 terminal resistance, #2 apply a powerful AC oscillator (audio or RF) and detect the field with an amplifier and headset like used to telephone lines. I found an old Fluke 8842A DVM in my pile of old equipment, it can read milliohms (4 terminal 4 lead measurement). I will check loop resistance from both near and far end and calculate, #12 ga has 1.588 Ohm/1000 ft. Just by comparing the near/far resistance I may get a clew, which section to replace and if the short is accessible in an elbow or junction. Cheers, Jon
 

· Registered
Joined
·
2,321 Posts
"Just by comparing the near/far resistance I may get a clew, which section to replace and if the short is accessible in an elbow or junction. "

But you just wrote that there are no pull elbows and no junctions.

Don't forget that there may be more than one short, or potential short, and fixing one damaged section may not be the end of it. Jobs that are done badly have a tendency to outwit all who try to apply logic. What if you locate the area, and find the insulation was stripped back for several feet? This is common in pulls with too many bends or where the conduit has sharp edges left in.

I think you'll best serve your customer by recommending a complete replacement of the conduit and wiring with a system that meets code.
 

· Registered
Joined
·
1,827 Posts
I think you'll best serve your customer by recommending a complete replacement of the conduit and wiring with a system that meets code.
Couldn't agree more. When I see an installation that is so bad I can't do a guaranteed a repair. I recommend replacement and give my price. Any splice to NM underground will not be code compliant and I would not be able to guarantee it so I would price replacing the whole thing.

Add a junction box in both buildings where the conduit exits the building. would allow you to replace the underground and splice it. But if even the inside install is really bad I would replace that too.

Any pictures of this install?
 

· Registered
Joined
·
12,388 Posts
Hello all: I have a 12/3 run of about 60' partly indoors and partly in a PVC conduit. Problem: there is a short from ground to neutral. Question: How to locate the short: Most of the equipment to locate cables and shorts is very costly. Any way to deduct the distance from the end to the short? Kind Regards, Jon
At that distance, pulling in three new wires would be quicker than posting on this forum.:thumbsup:
 