Appliance pigtail-receptacle for Dishwasher and 230V 30A rated 2 pole at H2O heater will eliminate the 422.31B requirement.Which code covers the need for a lock out on a dishwasher and on a water heater? Is it 422.31B? Never had to install a lockout on a dishwasher befor, first time i got giged on it.
More than that, you cannot simply put a 'Whirlpool' cord on a GE dishwasher.It is illegal to add a cord to a dishwasher if the d/w is not listed for a cord to be added. .
You have to use a cord that is a listed accessory for that particular DW.![]()
NOTHING more condescending then starting a reply with "Um"Um all applicances require a disconnect. For the d/w we mount a switch under the cabinet with the sink. On water heaters we mount non fuseable pull out on the wall next to it. Are you serious? You've never had to install disconnects?
True Bob, but I have yet to meet an inspector smart enough to know this. :no:More than that, you cannot simply put a 'Whirlpool' cord on a GE dishwasher.
Until that day comes I'll be installing "acme" cords knowing full well that the disahwasher can't read the name on the cord and won't be offended :thumbsup:
Um, have you read your own posts?NOTHING more condescending then starting a reply with "Um"![]()
Just pointing out the rules, what we all do with that info is up to us.True Bob, but I have yet to meet an inspector smart enough to know this. :no:
I generally stay out of this crap but since you're getting all wound up I would think any licensed electrician would know that a light fixture draws the same amount of power no matter what voltage it's wired for. :thumbsup:I would think any licensed electrician would know appliances need a disconnect you pathetic jackass. Why waste a receptacle and buy a cord when you could hard wire and be legal?
Because even a pathetic jackass is smart enough to know that a cord and receptacle is more cost effective than making a return trip to make connection after the plumber finally shows up to install the dishwasher. Same goes for disposals.I would think any licensed electrician would know appliances need a disconnect you pathetic jackass. Why waste a receptacle and buy a cord when you could hard wire and be legal?
What's that shorty, look up when you speak so I can hear you. :laughing:Um, have you read your own posts?
Um your as condescending as the rest of us. :laughing:
It's between me and the pathetic jackass that doesn't believe in god.:thumbsup:
Because even a pathetic jackass is smart enough to know that a cord and receptacle is more cost effective than making a return trip to make connection after the plumber finally shows up to install the dishwasher. Same goes for disposals.:
Who knew there was even a receptacle shortage. :no::
Now remember, watts are watts..... :laughing:
This is not a very Christian thing to say.!
So you look down on me because I don't believe in fairy tales? Who's the pathetic jackass?!
See you in hell sucker!
Don't be sorry, we love s**t, it is what we deal in here.Damn, ask a question and start a bar fight. I know about the disconnect for the water heater, but have never heard of a lock out. As far as the dishwasher goes have installed plenty and the breaker at the panel was always the disconnect, never told to put a switch under the sink. Sorry to ask a question and stir up so much s**t.
.. that can serve as the disconnecting means, but fewer and fewer appliances have a switch that qualifies.422.34 Unit Switch(es) as Disconnecting Means. A unit
switch(es) with a marked-off position that is a part of an
appliance and disconnects all ungrounded conductors shall
be permitted as the disconnecting means required by this
article where other means for disconnection are provided in
occupancies specified in 422.34(A) through (D).
422.31 Disconnection of Permanently Connected
Appliances.
(B) Appliances Rated over 300 Volt-Amperes or 1⁄8
Horsepower. For permanently connected appliances rated
over 300 volt-amperes or 1⁄8 hp, the branch-circuit switch or
circuit breaker shall be permitted to serve as the disconnecting
means where the switch or circuit breaker is within
sight from the appliance or is capable of being locked in the
open position. The provision for locking or adding a lock to
the disconnecting means shall be installed on or at the
switch or circuit breaker used as the disconnecting means
and shall remain in place with or without the lock installed.