Would re-lamping 50 watt halogen MR16 GU5.3 with 6 watt LED extend the life of the transformer given the reduced load? Unfortunately, I do not know what the transformer is.

Thank you in advance.

Van
 

·
Administrator
Retired EC
Joined
·
23,167 Posts
You must use the appropriate LED driver to run them. A standard LV transformer is not what you use for LED.
 