I have a 3phase 4 wire 120/208 panel fed from a transformer that is fed from a 277/408 panel. We turned it on and while testing voltage at a receptacle, it read 60v. I won't be back to trouble shoot til Tuesday but I can't stop thinking about it. Two explanations that I could think of is a loose neutral, or insufficient bonding of the neutral to ground from the xfmr. What are your opinions on these theories?
1 - 8 of 8 Posts
One of your phases has completely dropped out perhaps?
Line to neutral or line to ground?
Haven't done any measurements myself but I was told line to neutral
If that is a line to neutral voltage then the transformer bonding and grounding has nothing to do with the issue.
Need to do L-N, N-G, L-G and use a low impedance tester.
I'm thinking either open neutral or you actually have a dead circuit and you're just seeing ghost voltage.