You can look into buying a 250 amp breaker that will fit in that panel, then why not?
You can look into buying a 250 amp breaker that will fit in that panel, then why not?Hi.
I have some electrical drawings that has a MCC with 3 control panel with a 150A breaker, 50A, 20A and a hoist with a breaker of 20A all individually connected to the same bar (sum of 240). The main breaker of the MCC is 400A. Can I lower the main breaker capacity to 250A? Is there a formula or a NEC table I should go by?
Probably just to have the power available.I was just wondering why the designer used a 400A main breaker.
The ampacity of the breakers have nothing to do with sizing the panel. The size is based on the calculated load. Why would you change a 400 amp panel into a 225 amp panel? especially if it is designed for 400 amps. Think of future use.So if it's greater that the sum of the Ampacities is OK?
Hi.
I have some electrical drawings that has a MCC with 3 control panel with a 150A breaker, 50A, 20A and a hoist with a breaker of 20A all individually connected to the same bar (sum of 240). The main breaker of the MCC is 400A. Can I lower the main breaker capacity to 250A? Is there a formula or a NEC table I should go by?
The ampacity of the breakers have nothing to do with sizing the panel. The size is based on the calculated load. Why would you change a 400 amp panel into a 225 amp panel? especially if it is designed for 400 amps. Think of future use.
But isn't the customer paying for a 400a panel? This is most likely for future. I'm sure you are going to pass on the savings to the customer if you reduce the panel size?Guy said:Cost