I find myself in new territory again. While the physical work is no problem, I need to provide a load calc for this new service.

Power source is 120/208 to a 200 amp meter which will feed a 200 amp MB outdoor panel. Here is where im unsure of how to calculate. The panel will be feeding receptacles for the boats. 6-30 amp 3 wire and 8-standard 20 amp gfci outlets.
I know a dryer is 5000 watts and a fridge is 1200 watts and so on.
What do I use as a measure for the 30 amp boat receptacles?

Thanks for any code ref you can provide
 

·
Premium Member
Joined
·
20,088 Posts
There is a calculation for de-rating receptacles.
It's in the NEC under "Marinas" it's an easy read.
I have 4 50 amps on one dock and it required 200 amps.
They each have a 50 amp twist lock and a separate 20 amp GFI receptacle.
I was required to only count the 50 for the calculations.

How are your receptacles configured, do you have some 50 amp docks and some 30s or does each dock have a choice?
 

·
Registered
Joined
·
232 Posts
Discussion Starter · #3 ·
No 50s. These outlets are basically for dry dock repairs. All the outlets will be mounted on a wall and clients will roll out cords while working on boats and roll back up when repairs are done.
 

·
Registered
Joined
·
97 Posts
I find myself in new territory again. While the physical work is no problem, I need to provide a load calc for this new service.

Power source is 120/208 to a 200 amp meter which will feed a 200 amp MB outdoor panel. Here is where im unsure of how to calculate. The panel will be feeding receptacles for the boats. 6-30 amp 3 wire and 8-standard 20 amp gfci outlets.
I know a dryer is 5000 watts and a fridge is 1200 watts and so on.
What do I use as a measure for the 30 amp boat receptacles?

Thanks for any code ref you can provide

Try 555.12
 

·
Premium Member
Joined
·
20,088 Posts
No 50s. These outlets are basically for dry dock repairs. All the outlets will be mounted on a wall and clients will roll out cords while working on boats and roll back up when repairs are done.
Ok so, don't let me lead you to slaughter here but this in the way we just figured our dry dock receptacles.

There is no limit on dry dock.
This is the reasoning.
Is you have small boats, they are being used for lighting. Same thing for big boats.
Air conditioning units are usually water cooled and if these need service, it is rare and won't be on very much at all.
You might be running some battery tenders on bigger boats.

The only reason that you would need 30s or 50s is that boat cords, aka shore power, is what someone would expect to find out in the wild and most all boats have these configurations and carry adapters for where they don't.

Your load couldn't be 30 amps in dry dock. If a boat is really big, they will have a couple of 50s plugged into a magic box to make it 100 amps and everybody will know about it.

Right now I have about six 50' plus boats plugged in and all together they pull about 30 to 50 amps depending on what tools the guys are using.

So, lots of little boats, little power consumed per sf of yard. Big boats take up more space, might have a fridge running, lights and battery tender. All about the same until the portable welder comes out of the tool shed.
 

·
Registered
Joined
·
12,167 Posts
Since this is dry dock repairs, does 555 even apply?

If people are working on their boats with this power, does it need to be GFCI protected?
 

·
Registered
Joined
·
12,167 Posts
Here, the 20amp 120 volt have a GFI but not for the power outlets.
I understand, but these outlets are for people working on boats, no? If someone is plugging an adapter into a 30-amp receptacle and running a drill or sander or ??? then they won't have the GFI protection.

I've never seen receptacles in dry dock locations. The dry dock locations I've seen don't really allow for people to work on their boats, they had a boatyard type area for that. I'm a little confused about the OP's application.
 

·
Registered
Joined
·
232 Posts
Discussion Starter · #9 ·
Not being a boat guy I didn't use the right terms. The area is in the boat yard.
I read the entire 555 art. I learned a lot, thanks.

Lets say im treating it like a marina.

6- 30 amp 120 volt circuits = 21,600 va
6- 20 amp 120 volt circuits = 0 va (they don't count if im reading right.)
Apply 90% demand factor = 19440
which of the below is correct
19440 va divided by voltage 208 volts = 93 amps
or
19440 va divided by voltage 120 volts = 162 amps
 

·
Registered
Joined
·
12,167 Posts
Not being a boat guy I didn't use the right terms. The area is in the boat yard.
I read the entire 555 art. I learned a lot, thanks.

Lets say im treating it like a marina.

6- 30 amp 120 volt circuits = 21,600 va
6- 20 amp 120 volt circuits = 0 va (they don't count if im reading right.)
Apply 90% demand factor = 19440
which of the below is correct
19440 va divided by voltage 208 volts = 93 amps
or
19440 va divided by voltage 120 volts = 162 amps
I would do it like this.

19440/(208*1.732)=54A

19440/120/3(phases)=54A

This of course assumes that you can perfectly balance the loads.

Edit: I went back and looked at the OP again, the voltage was stated as 120/208 instead of 208Y/120. So based on that, I would do it this way.

19440/120/2(120V legs) = 81A. The neutral will carry about the same load as the ungrounded conductors since it's derived from a Y distribution.
 

·
Registered
Joined
·
97 Posts
Since this is dry dock repairs, does 555 even apply?
555 covers Marinas and boatyards, to me a boatyard, laydown area, haulout, etc. are all the same.

An angle grinder is around 7amps running and air compressor 15amps?

I'm not sure if an electrician or an engineer can call out the horse**** "load diversity" part of the code, but it might be something worth talking to the AHJ about

Whatever you do, I'd advise not to go hack and use aluminum wiring in a marina
 

·
Registered
Joined
·
232 Posts
Discussion Starter · #12 ·
I would do it like this.

19440/(208*1.732)=54A

19440/120/3(phases)=54A

This of course assumes that you can perfectly balance the loads.

Edit: I went back and looked at the OP again, the voltage was stated as 120/208 instead of 208Y/120. So based on that, I would do it this way.

19440/120/2(120V legs) = 81A. The neutral will carry about the same load as the ungrounded conductors since it's derived from a Y distribution.

It is 120 volt on each leg. It is a 4 wire system.
 

·
Registered
Joined
·
12,167 Posts
It is 120 volt on each leg. It is a 4 wire system.
OK, so it's a 208Y/120 system (indicates a 4-wire system) instead of a 120/208 system (which indicates a 3-wire system).

Then I stick with the 54-amp calculation.
 

·
Registered
Joined
·
232 Posts
Discussion Starter · #14 ·
OK, so it's a 208Y/120 system (indicates a 4-wire system) instead of a 120/208 system (which indicates a 3-wire system).

Then I stick with the 54-amp calculation.
Customer just requested that I change the quote to 12- 30 amp 120 volt recepts and zero 120 volt
So now my calc would look like this?
30x120=3600 VA per recep
3600x12=43200 VA total
80% per table = 34560 VA
34560 VA / 120 x 3 legs =96
 

·
Registered
Joined
·
12,167 Posts
Customer just requested that I change the quote to 12- 30 amp 120 volt recepts and zero 120 volt
So now my calc would look like this?
30x120=3600 VA per recep
3600x12=43200 VA total
80% per table = 34560 VA
34560 VA / 120 x 3 legs =96
The answer looks right, but, the order of operations for what you wrote would not equal what you got. It should be written 34560/(120*3) or 34560/120/3

Another way you could do it is 30A * (12/3 phases) * .8 = 96A
 
  • Like
Reactions: Shawn23

·
Registered
Joined
·
232 Posts
Discussion Starter · #16 · (Edited)
Back to square one

Now we are building a new service so she can have the 50 amp 250 volt recepts. Customer is now talking about installing pedestals. One side with a 50 amp 240v, 30 amp 120v and the other side with a 30 amp 120v and 20 amp gfci.
Total of 4 pedestals
Am I correct that each pedestal will require 15,600VA/240V = 65 Amps each.
65 amps*4= 260 total amps.
I did not use a demand factor due to only having 4 or less of each?
 

·
Registered
Joined
·
97 Posts
Now we are building a new service so she can have the 50 amp 250 volt recepts. Customer is now talking about installing pedestals. One side with a 50 amp 240v, 30 amp 120v and the other side with a 30 amp 120v and 20 amp gfci.
Total of 4 pedestals
Am I correct that each pedestal will require 15,600VA/240V = 65 Amps each.
65 amps*4= 260 total amps.
You would only calculate the highest amperage recep per slip/stall or whatever each space is called
 

·
Registered
Joined
·
12,167 Posts
Now we are building a new service so she can have the 50 amp 250 volt recepts. Customer is now talking about installing pedestals. One side with a 50 amp 240v, 30 amp 120v and the other side with a 30 amp 120v and 20 amp gfci.
Total of 4 pedestals
Am I correct that each pedestal will require 15,600VA/240V = 65 Amps each.
65 amps*4= 260 total amps.
It sounds like you have a 50/30 side A and 50/30 side B. You would take the highest rated receptacle per side, so 50+50 = 100. 100*240 = 24kVA per pedestal (which serves 2 slips).

A couple of things. The 50-amp is normally a 120/240 receptacle and not a 240 receptacle (actually it's rated 125/250). Make sure to include the neutral in your cable.

Although it's done a lot, feeding a 120/240 receptacle with 120/208 is a code violation. See 555.19(A)(3).
 