Does anyone know where you can apply the higher ampacities listed in table 2 for 14 / 12 / 10 AWG?
 

·
Light Bender
plumber
Joined
·
5,878 Posts
When u have to derate a conductor because there are more than 3 in a conduit you can start with the ampacity in the 90 degree column. Assuming your using a 90 degree rated conductor.
 

·
Senile Member
I make all the electrons line up for their Flu shots
Joined
·
30,876 Posts
Does anyone know where you can apply the higher ampacities listed in table 2 for 14 / 12 / 10 AWG?

When wiring some AC and Refrigeration compressors you can use the higher values . Only some.
 
  • Like
Reactions: Bst

·
PPE Saves Fingers
Joined
·
291 Posts
Does anyone know where you can apply the higher ampacities listed in table 2 for 14 / 12 / 10 AWG?
When derating is nessisary, or when a code rule requires you to calculate the required wire size for a given situation.

Off hand, that's motors, capacitors, heat, welders and transformers.
 