Max Number Of Receptacles on GFI Protected Circuit?

70K views 143 replies 36 participants last post by  zen 
The code allows you to load a circuit to 80% of its overcurrent rating and each receptical is counted as 180 Watts' so 15A X 120V = 1800 Watts/.8= 1440 Watts=180= 8 recepticals

20A X 120V = 2400 Watts X .8 = 1920/180 =10.6

Remember these are the minimum requirements I have always use 75% instead of 80.
so, if you had a customer in a home that wanted a new receptacle added in an upstairs bedroom, and the panel is in the basement, and the existing circuit has let's say 10 receptacles and a couple of lights on it but nothing much being plugged into these outlets, are you going to add a new circuit for this? If so then great as long as you have no problem selling this to the homeowner, but I would never even try to do this. I would simply tap off of the existing, as I can sleep knowing that I did the job correctly and didn't overkill it and rip off the HO.
 