Its up to 36 at one building. I dont know why but I think its 36 for some reason.
42 does not even come into play now.You could load a main lug panel with 42 breakers if the it's in the same structure as the main.
Your question is poorly written and not specific enough to help you with your query. It is also poor etiquette to post such a rude reply to someone who was trying to answer your question.
That is true...it was just a number that the OP cited and force of habit.42 does not even come into play now.
read 230.71 per the ops ref....Don't listen to any of these rascals, I don't think they understand your question.
If your question is "Why can you have 6 circuits fed without a main?" The answer is so the fire dept can come and throw 6 switches and have the structure dead. As soon as you need 7 circuits, you will need a main.
I stand by my statement.read 230.71 per the ops ref....
Yes. Good work HawkShock. This applies to "Service Disconnecting Means". Each one of the 6 will need to have a sticker that identifies it as such.Don't listen to any of these rascals, I don't think they understand your question.
If your question is "Why can you have 6 circuits fed without a main?" The answer is so the fire dept can come and throw 6 switches and have the structure dead. As soon as you need 7 circuits, you will need a main.
Meaning, YOU DON'T NEED a main breaker if you are feeding 6 or less circuits.
Are you implying that any main lug panel with more than 6 breakers is a code violation?I stand by my statement.
yes I agree with it as "you" wrote it the op seems as mac said mixing up 2 different refs:thumbsup:I stand by my statement.
Not at all.Are you implying that any main lug panel with more than 6 breakers is a code violation?
That would only be true if a main lug panel with 7 or more breakers were used as a service entrance. SERVICE DISCONNECTING MEANS vs. Interior distribution/branch OCPDs seems to be adding confusion here.Are you implying that any main lug panel with more than 6 breakers is a code violation?
That would only be true if a main lug panel with 7 or more breakers were used as a service entrance. SERVICE DISCONNECTING MEANS vs. Interior distribution/branch OCPDs seems to be adding confusion here.