nail it, screw it.

I dont get question?

Metallic cable needs a metal box for one, what difference does it make how you secure it? [doesn't it? I wouldn't do it any other way]

and then bond it.
 

· Salty Member
Joined
·
31,030 Posts
Bonded or grounded?
Bonded

314.3 Nonmetallic Boxes. Nonmetallic boxes shall be permitted
only with open wiring on insulators, concealed knoband-
tube wiring, cabled wiring methods with entirely nonmetallic
sheaths, flexible cords, and nonmetallic raceways.

Exception No. 1: Where internal bonding means are provided
between all entries, nonmetallic boxes shall be permitted
to be used with metal raceways or metal-armored
cables.

Exception No. 2: Where integral bonding means with a
provision for attaching an equipment bonding jumper inside
the box are provided between all threaded entries in
nonmetallic boxes listed for the purpose, nonmetallic boxes
shall be permitted to be used with metal raceways or metalarmored
cables.
 

· RIP 1959-2015
Joined
·
39,532 Posts
It seems as though this means a metallic strap or something inside of the box.??
MC cable sheath is a chitty ground so article 250 does not allow it to be used as such,but it is a metal raceway so it still must be bonded together,the grounding conductor will provide a Better path back to ground,with the sheath of MC Cable without having the grounding conductor bonded to it by connection to the box that sheath would be glowing red hot with a low amount of current running through it just a few amps so the circuit breaker will not Tripp.
 

· ET rocks
Joined
·
2,864 Posts
Oh stop, like you haven't done there before :whistling2:


The sheath is bonded on the panel side of the run :thumbup:
:laughing:

i haven't. What would be the scenario to use both together? Ran out of cable or ran out of 1900's?

Do you guys use an anti-short and tape? Hack-a-tha's
 

· Banned
Joined
·
746 Posts
:laughing:

i haven't. What would be the scenario to use both together? Ran out of cable or ran out of 1900's?

Do you guys use an anti-short and tape? Hack-a-tha's
It sounds so strange I didn't even think it would be legal, much less ever need to look it up. & find out you can do it.:laughing:
 

· Banned
Joined
·
746 Posts
I need a picture of someones install doing this MC to a plastic box just so I can fully grasp how stupid it would look.
 
  • Like
Reactions: BBQ and 3xdad

· Registered
Joined
·
3,596 Posts

· Banned
Joined
·
746 Posts
Arlington makes a recessed Weatherproof In use box that is plastic.

I ran MC to it.

http://www.wescodirect.com/direct/images/products/pdf/164_Elec08.pdf
no disrespect, something like that? ok if you feed from behind in wall. I will never be able to wrap my head around plastic stuff. doubt it would pass around here. the weather extremes would probably destroy it here.

my gist of this thread is a nail up plastic box for rope type installs with MC.

I never saw a plastic box or romex until about 10 yrs in the trade. saw a lot of K & T, but never the wiring practices y'all see as normal.

just can't get my head around it.
 
  • Like
Reactions: therain