This thread is for the discussion of medical care facility, healthcare facilities, patient recovery rooms, dental offices and everything in-between that may be related.

Feel free to ask questions and answer if you can provide NEC references to your answers that would be helpful too.
 

· Pool Shark
Joined
·
472 Posts
Discussion Starter · #2 ·
I've not gotten the 2014 code yet but the 2011 makes some interesting requirements for the double-redundancy grounded MC cable or as you may know it HCF MC cable.

The 2011 NEC makes it clear that the use of isolated grounded outlets are not viable for the safety of patients, medical staff and their equipment, and they are not permitted to be installed anymore for such uses.

That being said, has anybody heard of any new 2014 changes to the medical health care areas?
 

· RIP 1959-2015
Joined
·
39,532 Posts
Here is one more...


517.18 General Care Areas.
(A) Patient Bed Location. Each patient bed location shall be supplied by at least two branch circuits, one from the critical branch and one from the normal system. All branch circuits from the normal system shall originate in the same panelboard. The electrical receptacles or the cover plate for the electrical receptacles supplied from the critical branch shall have a distinctive color or marking so as to be readily identifiable and shall also indicate the panelboard and branch-circuit number supplying them.
Branch circuits serving patient bed locations shall not be part of a multiwire branch circuit.
Exception No. 1:  Branch circuits serving only special purpose outlets or receptacles, such as portable X-ray outlets, shall not be required to be served from the same distribution panel or panels.
Exception No. 2:  The requirements of 517.18(A) shall not apply to patient bed locations in clinics, medical and dental offices, and outpatient facilities; psychiatric, substance abuse, and rehabilitation hospitals; sleeping rooms of nursing home;, and limited care facilities meeting the requirements of 517.18(B)(2).
Exception No. 3:  A general care patient bed location served from two separate transfer switches on the critical branch shall not be required to have circuits from the normal system.
(B) Patient Bed Location Receptacles. Each patient bed location shall be provided with a minimum of eight receptacles. They shall be permitted to be of the single, duplex, or quadruplex type or any combination of the three. All receptacles shall be listed “hospital grade” and shall be so identified. The grounding terminal of each receptacle shall be connected to an insulated copper equipment grounding conductor sized in accordance with Table 250.122.
Exception No. 1:  The requirements of 517.18(B) shall not apply to psychiatric, substance abuse, and rehabilitation hospitals meeting the requirements of 517.10(B)(2).
Exception No. 2:  Psychiatric security rooms shall not be required to have receptacle outlets installed in the room.
Informational Note:  It is not intended that there be a total, immediate replacement of existing non–hospital grade receptacles. It is intended, however, that non–hospital grade receptacles be replaced with hospital grade receptacles upon modification of use, renovation, or as existing receptacles need replacement.
(C) Designated General Care Pediatric Locations. Receptacles that are located within the patient rooms, bathrooms, playrooms, and activity rooms of pediatric units, other than nurseries, shall be listed tamper-resistant or shall employ a listed tamper-resistant cover. [99:6.3.2.2.6.2(F)]
 

· RIP 1959-2015
Joined
·
39,532 Posts
What do you think of running EMT with a secondary ground in lieu of HFC MC cable?
As long as all of the connections are rock solid,I would say it's better,but it's more labor intensive too,but if you can sell it,it's more profit:)
 

· Registered
Joined
·
3,601 Posts

· RIP 1959-2015
Joined
·
39,532 Posts
If 517.18 (B) requires 8 receptacles (4 in 2011) how many are required in the critical care area?(517.19) (B)
517.19 Critical Care Areas.

(B) Patient Bed Location Receptacles.
(1) Minimum Number and Supply. Each patient bed location shall be provided with a minimum of 14 receptacles, at least one of which shall be connected to either of the following:
 