Discussion Starter · #1 ·
I'm hooking up a big metal punching machine (Scotchman 5014-TM).
It's a 3 phase hookup. Sheet shows 3 hp 3 ph (2.24 kW)
The school has 3 ph 208.
Am I correct in finding amps by figuring 2,240/208?
I came up with 10.7
Seems I'm forgetting something.
 

·
Bilge Rat
motors and controls.........
Joined
·
8,403 Posts
In actual reality, a 3HP motor will be somewhere around 8 amps.

The voltage/KW calcs don't include power factor.
 

·
Registered
Joined
·
8,050 Posts
micromind said:
In actual reality, a 3HP motor will be somewhere around 8 amps. The voltage/KW calcs don't include power factor.
True. But when hooking up industrial type machinery wouldn't you just go off the kW listed on the nameplate?
 

·
Registered
Joined
·
8,050 Posts
micromind said:
When motors are rated in KW, the KW rating is what appears at the shaft, not the input.
Could you explain further please? When I hook up machines (like a laser) that has maybe 15 motors in it I'm not even looking at the motor nameplates. Usually there is one nameplate with a total kW on it and that's what I figure it for.
 

·
Registered
Joined
·
5,512 Posts
This k.w. thing now isn't burned into my brain like amps on nameplates were that I grew up with.
In places OTHER than North America, the kW rating on a motor nameplate is used as a MECHANICAL rating in the same way we show HP on a motor nameplate. It's only relevant to shaft torque and speed, not ELECTRICAL kW. The ELECTRICAL kW rating would be what they refer to as the "Absorbed power".

But if you are looking at a nameplate for a machine or system that has multiple loads connected to the same main incoming terminals, and the kW rating is referring to the entire machine, then that is the ELECTRICAL kW rating of the machine.

Now if you are wanting to size anything for your punch and this information is coming from the single motor on it, the other stuff is actually somewhat irrelevant anyway. The NEC does not ask you to calculate FLA. You have to size the conductors, OCPD etc. based on the motor HP rating. That's easier; there are 746W / HP. So 2.24kW = 2240W / 746 = 3.002HP, or 3HP. You then use the charts in Article 430 to size things based on 3HP.
 

·
Registered
Joined
·
8,050 Posts
I don't think it'd matter much but I'd do it the way I described. The overloads are sized by the FLC listed on the motor and the current rating on the breaker won't matter much if you size it to the full 250%
 

·
Bilge Rat
motors and controls.........
Joined
·
8,403 Posts
Here's the codebook version for a 3HP 3ø motor on 208, assuming it's just the motor and nothing else except a control transformer.

1) 430.6(A)(1) states that table values are to be used, or the nameplate, whichever is greater.

2) Table 430.250 lists a 3HP 3ø motor operating on 208 as 10.6 amps.

3) 430.22(A) states that for a single motor, the table value must be multiplied by 1.25 to get the minimum wire size.

4) 110.14(C)(1)(a)(4) states that wire is to be sized based on 75ºC, unless any part of it is rated less.

5) 240.4(D) and (G) state that the 15, 20, and 30 amp limitations to 14s, 12s, and 10s do not apply to motors.

6) 10.6 X 1.25 = 13.25; Table 310.16 lists #14 at 20 amps, therefore this is the minimum wire size.

7) Table 430.52 lists the maximum size of a basic circuit breaker as 250% of the value in Table 430.250. 10.6 X 2.5 = 26.5 430.52(C)(1) Exception #1 allows the use of the next standard breaker if the calculated value does not correspond to a standard value, so the maximum breaker would be 30 amp.

8) Yes, you can have a 30 amp breaker and #14s. But 14s are the minimum (there's no maximum), and a 30 is the maximum (there's no minimum). Personally, I'd use 14s or 12s and a 15 or a 20.

9) 430.6(A)(2) states that the overloads need to be based on nameplate current.

There, wasn't that easy; 9 steps and 4 different articles just to hook up a dumb motor.....
 

·
Registered
Joined
·
2,325 Posts
So that's why the engine in my Italian tractor is rated in KW.
The EU only uses HP as a secondary rating to watts, as of 2010.

The concept of how James Watt originally calculated horsepower is fairly ridiculous, and reads a little like the witch scene in Monty Python and the Holy Grail.
 

·
Registered
Joined
·
539 Posts
Discussion Starter · #18 ·
micromind said:
Here's the codebook version for a 3HP 3ø motor on 208, assuming it's just the motor and nothing else except a control transformer. 1) 430.6(A)(1) states that table values are to be used, or the nameplate, whichever is greater. 2) Table 430.250 lists a 3HP 3ø motor operating on 208 as 10.6 amps. 3) 430.22(A) states that for a single motor, the table value must be multiplied by 1.25 to get the minimum wire size. 4) 110.14(C)(1)(a)(4) states that wire is to be sized based on 75ºC, unless any part of it is rated less. 5) 240.4(D) and (G) state that the 15, 20, and 30 amp limitations to 14s, 12s, and 10s do not apply to motors. 6) 10.6 X 1.25 = 13.25; Table 310.16 lists #14 at 20 amps, therefore this is the minimum wire size. 7) Table 430.52 lists the maximum size of a basic circuit breaker as 250% of the value in Table 430.250. 10.6 X 2.5 = 26.5 430.52(C)(1) Exception #1 allows the use of the next standard breaker if the calculated value does not correspond to a standard value, so the maximum breaker would be 30 amp. 8) Yes, you can have a 30 amp breaker and #14s. But 14s are the minimum (there's no maximum), and a 30 is the maximum (there's no minimum). Personally, I'd use 14s or 12s and a 15 or a 20. 9) 430.6(A)(2) states that the overloads need to be based on nameplate current. There, wasn't that easy; 9 steps and 4 different articles just to hook up a dumb motor.....
No doubt
I was gonna throw it on a 20A/#10
 

·
Registered
Joined
·
5,512 Posts
Ok,
So are we going with 6.23A, 8A, no Amps, or what?
I love this forum, but where's the final answer??
FLC for a 3 phase motor (as opposed to the nameplate FLA, since you apparently don't have it) can be ESTIMATED using the following formula:

A = (746 x HP) / (1.732 * Volts * Efficiency * Power Factor

You don't know the efficiency or power factor of your motor, otherwise you would have the FLA as well. So the best you can do is guess by ASSuming 90% efficiency (if it is less than 10 years old, 80% if it is older) and a .8 power factor.

A = (746*3)/(1.732 * 208 * .9 * .7)

A = 2238 / 259.38

A = 8.63A
 

·
Registered
Joined
·
539 Posts
Discussion Starter · #20 ·
JRaef said:
FLC for a 3 phase motor (as opposed to the nameplate FLA, since you apparently don't have it) can be ESTIMATED using the following formula: A = (746 x HP) / (1.732 * Volts * Efficiency * Power Factor You don't know the efficiency or power factor of your motor, otherwise you would have the FLA as well. So the best you can do is guess by ASSuming 90% efficiency (if it is less than 10 years old, 80% if it is older) and a .8 power factor. A = (746*3)/(1.732 * 208 * .9 * .7) A = 2238 / 259.38 A = 8.63A
Your right, apparently-I don't have it, Jr

Who's ASS..? uming

It's a brand new unit, I'm going by info given on the spec. sheet.

I bet I'll be fine with #10 on a 20A.
APPARENTLY

I appreciate help, but don't appreciate sarcastic attitude or being called an ass.

Frustrated I can't get a clear answer? Yes
Ticked that someone's getting mad about it? APPARENTLY!
 