369 Views 6 Replies 4 Participants Last post by  radio208
Im taking over a 6 gang meter with 3 meters left for release. My question is for those meters to be released do i need to have the subpanel with its circuits already ran or can the subfeed just be connected to the lugs?

See less See more
2
1 - 7 of 7 Posts
Im taking over a 6 gang meter with 3 meters left for release. My question is for those meters to be released do i need to have the subpanel with its circuits already ran or can the subfeed just be connected to the lugs?
View attachment 176702
View attachment 176701
ask the inspector
he is the only one who will have your answer
local inspector and local rules
it doesnt matter that it makes you feel uncomfortable
every body has to learn to start with

how ever in my area the job must be complete before the final inspection and the utility will supply the meter
Why no ground bar and ground in the panel shown?

What in the world is the "U" piece of plastic doing going from side to side?

I have never seen a ganged meter section with out main breakers. That requires unfused conductors from the meter to the main breaker in the public domain. Not something allowed where I live and work.

Are you working from approved plans or is someone making this up as they go?
Why no ground bar and ground in the panel shown?

What in the world is the "U" piece of plastic doing going from side to side?

I have never seen a ganged meter section with out main breakers. That requires unfused conductors from the meter to the main breaker in the public domain. Not something allowed where I live and work.

Are you working from approved plans or is someone making this up as they go?
The breakers are below the meters three and three
Cool beans could not see behind the door. Then the question becomes why do you have a main in the panel, the pic.
Cool beans could not see behind the door. Then the question becomes why do you have a main in the panel, the pic.
Im just arriving to the jobsite. That main panel will be changed.
Since it's been a few days...just what is the purpose of the 'U' between the 3 meter sides?