I'm getting tired of defending my HVAC circuits to HVAC installers who do not understand the meaning of MCA. Last week it was a mini split with a FLA of 9.3 and an MCA of 15. We ran #12s. The installer refused to connect it, saying it had to be #10 and he was not going to be responsible for damage to the unit or a fire.
Today another installer told a homeowner I should have ran #8s to his condenser with an MCA of 26 (30-40 foot run). We ran #10s. He told her I violated the NEC and the wire could start a fire because it is on a 40 amp breaker (per the nameplate). He said the warranty is void on the unit thanks to me. I haven't had a chance to speak to this guy yet.
Whaddya do?
Today another installer told a homeowner I should have ran #8s to his condenser with an MCA of 26 (30-40 foot run). We ran #10s. He told her I violated the NEC and the wire could start a fire because it is on a 40 amp breaker (per the nameplate). He said the warranty is void on the unit thanks to me. I haven't had a chance to speak to this guy yet.
Whaddya do?