Your best bet is to just install the fuse next to the switch box, feed the fuse with #14 then the #18 should be good.
Another way to go, nipple from the 4x4 to the transformer box and use #14 wire, or use a transformer that mounts right on the box, Hammond makes control transformers that mount like doorbell transformers.Your best bet is to just install the fuse next to the switch box, feed the fuse with #14 then the #18 should be good.
We typically use one of these styles to prevent any need to have 120vac freely wired inside our cabinets. We always keep anything over 24vac rated in a separate enclosure. So anyone working inside the main cabinet does not need to worry about any voltage greater then about 24vac.Another way to go, nipple from the 4x4 to the transformer box and use #14 wire, or use a transformer that mounts right on the box, Hammond makes control transformers that mount like doorbell transformers.
Class 2 Energy Limiting Box Mount (BF Series) - Hammond Mfg. (hammfg.com)
![]()
![]()
Looks nice enough.View attachment 166224
This is how we typically have the install setup to keep anything over 24vac separate.
LoL ... no sh1t !It's inside a cabinet but it's a field install by an electrician not an engineered install that has been pre approved for anything.
Which code can he not break?LoL ... no sh1t !
An engineer can do a lot of things, but he can't break code.
The one I posted earlier. Our section 16 (Class 1 2 and 3 circuits) can use reduced size wiring, but the code I posted is the feed for the primary of the Transformer in a class 2 circuit. Needs to be wired according to code (nothing smaller than # 14, be protected ... etc etc )Which code can he not break?
That’s simply not true to put it mildly. Engineers are not the AHJ and cannot bypass NEC where it is required. Control panels do not have to follow 409.22 (and thus 450) but they do have to follow some other Code. Inside Listed panels UL is typically the Code but it can follow other NRTL standards. These are more restrictive than NEC. The ampacity tables in UL 508A are the 60 C column.It’s inside the cabinet so an engineer can design anything he wants to sign off on.
I’m sure the insulation on that wire isn’t rated for it’s use.
Mostly because we have un skilled site staff and sometimes even Jr techs who think all small wiring is safe so the start sticking there fingers in the cookie jar lolThis is a very strange looking panel imo
Why do you have the 120v separated from everything else in the enclosure, inception style?
It's 2022, use fingersafe components and keep the wiring in seperate panduits
live and learn, live and let die LOLMostly because we have un skilled site staff and sometimes even Jr techs who think all small wiring is safe so the start sticking there fingers in the cookie jar lol
Does CEC not have something similar to this ""The one I posted earlier. Our section 16 (Class 1 2 and 3 circuits) can use reduced size wiring, but the code I posted is the feed for the primary of the Transformer in a class 2 circuit. Needs to be wired according to code (nothing smaller than # 14, be protected ... etc etc )
AskingAre you asking us or telling us?
Not in the CEC.Does CEC not have something similar to this ""
The input leads of a transformer or other power source supplying Class 2 circuits shall be permitted to be smaller than 14 AWG, if not over 12 inches (305 mm) long and if the conductor insulation is rated at not less than 600 volts. In no case shall such leads be smaller than 18 AWG.""