Problem solved for now, next.....They connected the motor back up and tested. This time all three legs were clear. No shorts. The motor has been running for a month no problem?
Try to explain? Ask me any questions.
Also worth noting, a Fluke 87 is a DMM, not a megger, so what it is reading is resistance to ground based on the energy in a 9V battery. A 480V VFD is sending DC pulses at roughly 75 times that potential into the windings, so it finds faults that a meter might miss. I always recommend using a 1,000V megger when testing motors run by VFDs, anything else is not truly useful information.Low insulation resistance doesn’t mean it can’t run just that there is a current leak from the coils to the frame. The obvious cause is damage to the ground wall insulation usually after it burns up but that’s not the only one. Any amount of moisture or contamination or scuffed or pinched insulation will do it too. Manufacturing errors are pretty common for instance. As an example I once went through 3 1 HP motors on a small fat pump in a row before we figured it out. Motors come in as standard bells. If customer wants C-face we knock the bell housing and bearing off and put on the C-face one. When we did the C-face fit differently. The coils were built sticking out too far so they were crushed and meggered bad and tripped the drive out once the C-face bell end was installed. Not your case but pointing out the kind of subtle stuff you can run into. Many times the only way to find it is a tear down at a motor shop.
Check ground current settings and actual reading at the drive because it’s not a “megger”. In fact it doesn’t even measure ground current. It simply sums the three phase currents together (as a vector) and trips if the resulting calculated current exceeds around 10-20% of the average. This is a much higher current than the micro amps that it takes to get a bad megger reading. Read the manual because there are lots of causes for unbalanced currents not just a bad motor or wiring.
JRaefAlso worth noting, a Fluke 87 is a DMM, not a megger, so what it is reading is resistance to ground based on the energy in a 9V battery. A 480V VFD is sending DC pulses at roughly 75 times that potential into the windings, so it finds faults that a meter might miss. I always recommend using a 1,000V megger when testing motors run by VFDs, anything else is not truly useful information.
Large motors can give you a false reading on a megger unless you leave the megger connected for a period of time. 100hp isnt that big so the megger probably needs 5-10 seconds.JRaef
I initially took readings with Fluke 87 when called. Its just something I carry with me in the Plant for breakdowns. I took it for granted when I said megged motor that there would be an understanding I used a megohmmeter. (I'll take the hit, my fault).
But JRaef I like your tenacity. I megged at 1000 V, found short on all three legs. (measured at studs in pecker-head with leads feeding motor disconnected).
My question for you JRaef. What would you do next?
"Keep the comments coming"
In a perfect world that is true. Then one day you find only one phase grounded and you realize that the vfd only lists one fault when it dam well knows that the motor has both a short to ground and a open phase.I just don't understand why people megger all 3 leads on a 3 phase motor. If one phase is grounded, all 3 will be. If one phase is good, all 3 will be.
Most likely force of habit.I just don't understand why people megger all 3 leads on a 3 phase motor. If one phase is grounded, all 3 will be. If one phase is good, all 3 will be.
I just don't understand why people megger all 3 leads on a 3 phase motor. If one phase is grounded, all 3 will be. If one phase is good, all 3 will be.
I've read over this a few times, and I'm still mildly confused by this. After disconnecting the "T" leads at a VFD or Soft Start, if you are meggering them to ground from the starter, VFD, Soft Start or whatever runs the 3 phase motor, if you see a connection to ground there is a problem. Delta or Wye, it shouldn't matter, as you are meggering from one line through the cabling, the motor and back on the other two leads. A grounded winding or conductor anywhere along the system will show, unless there is a broken connection. Typically, before I megger I do a quick ohm reading between all 3 conductors to see if there is a notable difference indicating a broken wire.Six or 12 lead motors tested at the motor. Testing one lead only works if all the groups are wired together.
Also if you run into a 6 or 12 lead wye when the neutral is grounded you have to lift the ground first in addition to disconnecting VFDs and sift starts. I see these once in a while with CTs (differential protection) on large motors or goofy remote overload wiring when engineers overthink it.
Disconnected at the motor. All 6 or 12 leads disconnected from each other and separately megged.I've read over this a few times, and I'm still mildly confused by this. After disconnecting the "T" leads at a VFD or Soft Start, if you are meggering them to ground from the starter, VFD, Soft Start or whatever runs the 3 phase motor, if you see a connection to ground there is a problem. Delta or Wye, it shouldn't matter, as you are meggering from one line through the cabling, the motor and back on the other two leads. A grounded winding or conductor anywhere along the system will show, unless there is a broken connection. Typically, before I megger I do a quick ohm reading between all 3 conductors to see if there is a notable difference indicating a broken wire.
On any motor, I would be meggering all of the conductors that go to the motor, a two speed motor comes to mind really quickly.
If you are meggering with the VFD or Soft Start connected, you may end up chasing your tail on electronics and the inner workings of the controller. If they are unhooked, there is no doubt in what you are checking.
Perhaps I'm way off, as I've only had one coffee so far this morning.