I am trying to control one motor operated damper from two separate exhaust fans on two separate circuits. These dampers need to operate so that they actuate when either or both fans are running. How can I do this. The dampers are 120 volt.
Using an aux contact on the exhaust starters pass them to a relay that allows the damper motor to operate.snadeau said:I am trying to control one motor operated damper from two separate exhaust fans on two separate circuits. These dampers need to operate so that they actuate when either or both fans are running. How can I do this. The dampers are 120 volt.
Is this a real world job or a classroom project?I am trying to control one motor operated damper from two separate exhaust fans on two separate circuits. These dampers need to operate so that they actuate when either or both fans are running. How can I do this. The dampers are 120 volt.
What are relay's listed for if not for control of devices in the field?Relays, diodes etc would not be "listed" so would require field labeling by an NTRL recognized outfit, which might run your costs up.
What are relay's listed for if not for control of devices in the field?
I agree that the best way would be to use aux contacts on the exhaust fan starters. If the exhaust fans don't have starters, 2 RIB relays would do the job.
I was wondering about the separate circuit comment, problem about back feed to the other circuit, argument with the inspector etc.What are relay's listed for if not for control of devices in the field?
I agree that the best way would be to use aux contacts on the exhaust fan starters. If the exhaust fans don't have starters, 2 RIB relays would do the job.
I like this idea.If the exhaust fans don't have starters, 2 RIB relays would do the job.
Everyone should have a few RIB's on hand.2 RIB relays would do the job.
You are assuming there are mag motor starters involved.I don't get why this is so complicated. Aux contact of each starter to a relay coil.
OK, I've not done much HVAC stuff so I bow to the superior experience here. But would they be big enough to have motorized dampers associated with them? From what I've seen, small stuff like that usually just has gravity dampers.You are assuming there are mag motor starters involved.
I work with tons of roof mounted exhaust fans that do not use magnetic motor starters. Just simple wall switches.