Electrician Talk banner
1 - 11 of 11 Posts

· Registered
Residential & light commercial electrical contractor
Joined
·
70 Posts
Discussion Starter · #1 ·
Imagine a house with a properly installed main panel. I have to add a sub panel because the main panel is full. If all the ground bars were full would it be code compliant to add a double lug to the panel case and land both the ground and neutral of the sub panel to that lug? Would that cause the neutrals and grounds of the sub to be joined at both the double pig and the original main bonding jumper?
 

· Banned
Joined
·
7,205 Posts
The main is the only place you should bring neutral and ground together. So if I understand you correctly, you want to tie the neutral and ground of the sub panel feed in the main at the same point?

Sounds good to me, though some sparky's recommend keeping neutral and ground electrically the same point, but physically separate points for troubleshooting.. I don't care about that, though.
 

· Registered
Joined
·
654 Posts
The sub-panel should have separate neutral and ground buses that do not connect. The neutral and ground wires in the sub-panel feeder should go back separately to the main panel and get connected into those neutral and ground buses, respectively. See NEC 250.30(A).
 

· Registered
Residential & light commercial electrical contractor
Joined
·
70 Posts
Discussion Starter · #4 ·
Pharon said:
The sub-panel should have separate neutral and ground buses that do not connect. The neutral and ground wires in the sub-panel feeder should go back separately to the main panel and get connected into those neutral and ground buses, respectively. See NEC 250.30(A).
They would be separate at the sub but would be connected at the same lug that ties to the main panel case. This would connect ground to neutral twice inside the main panel.
 

· Electrical Contractor
Joined
·
9,279 Posts
Imagine a house with a properly installed main panel. I have to add a sub panel because the main panel is full. If all the ground bars were full would it be code compliant to add a double lug to the panel case and land both the ground and neutral of the sub panel to that lug? Would that cause the neutrals and grounds of the sub to be joined at both the double pig and the original main bonding jumper?
I'd never do it this way! What happens if the screw holding your double lug comes loose? You don't want to go there. Install a separate ground bar in the main panel. Bond it to the existing ground bar with a piece of #8. Move some of the existing grounding conductors from the original ground bar to the new one, freeing up space on the existing one. Install your neutral and your grounding conductors feeding the new sub-panel to the existing ground bar. Clear?
 

· Registered
Residential & light commercial electrical contractor
Joined
·
70 Posts
Discussion Starter · #7 ·
wendon said:
I'd never do it this way! What happens if the screw holding your double lug comes loose? You don't want to go there. Install a separate ground bar in the main panel. Bond it to the existing ground bar with a piece of #8. Move some of the existing grounding conductors from the original ground bar to the new one, freeing up space on the existing one. Install your neutral and your grounding conductors feeding the new sub-panel to the existing ground bar. Clear?
Clear. Good point. Thank you, I'll do as you said. So technically it's not illegal then?
 

· Electrical Contractor
Joined
·
9,279 Posts
Clear. Good point. Thank you, I'll do as you said. So technically it's not illegal then?
I usually install separate ground bars in a main panel and land the grounding conductors on them. Even though the mounting screw bonds them to the existing ones through the panel frame, I still install jumpers. Just my practice. I had a local tell me that the mounting screw was no longer sufficient. Maybe someone has a code or maybe it's a local thing.
 

· Electrical Contractor
Joined
·
9,279 Posts
the sub-panel should have separate neutral and ground buses that do not connect. The neutral and ground wires in the sub-panel feeder should go back separately to the main panel and get connected into those neutral and ground buses, respectively. See nec 250.30(a).
250.32 (b) (1) is another one.
 